Hi

Went to look at a main combi 24 he boiler. The issue was hot water would only work with the heating on.

We had a look and from cold, ran the hot tap at the sink and it was going down the flow pipe. We changed the diverter and now the boiler would come on with a hw demand as normal but the water would be hot/cold. Cleaned the plate and everything was fine.

No issues for about 10 days, got a call to go back as hw not working again. Pin not coming out when demand put on. Checked filter all clear.

Manually operated micro switch and ran hot tap and its going down the flow again.

Ch works fine.

Any advice what next. Don't want to throw parts at it.

Thanks
 
Might have to tweak the microswitch if you have fitted a refurbishment kit as some of the pins seem to be of slightly different lengths thus when demand is put in it does not fully make the switch,
Cheers,
Andy
 
Might have to tweak the microswitch if you have fitted a refurbishment kit as some of the pins seem to be of slightly different lengths thus when demand is put in it does not fully make the switch,
Cheers,
Andy

I think he changed the complete DV?

Hydraulic venturi broken to bits?
 
It's the big diaphragm at the front, small at the back.

Haven't looked at the hydraulic venturi.

When you remove the dhw diagram. You’ll see the diverter valve (similar thing at a ideal logic) drain the boiler down. Undo the big nut at the front of the diverter remove the inners and clean them make sure there pristine. check the quality of the water too if it’s full of crap advice for a system flush and magnaclean to be installed.

I’d check the dhw diaphragm too. And grease it all up.
 
When you remove the dhw diagram. You’ll see the diverter valve (similar thing at a ideal logic) drain the boiler down. Undo the big nut at the front of the diverter remove the inners and clean them make sure there pristine. check the quality of the water too if it’s full of crap advice for a system flush and magnaclean to be installed.

I’d check the dhw diaphragm too. And grease it all up.

Thanks the diverter is brand new though. If the venturi is playing up would that make the hot water go down the flow?
 
Thanks the diverter is brand new though. If the venturi is playing up would that make the hot water go down the flow?

The Venturi is a part fan proving safety device.

Sounds like you’ve got a blocked plate to plate or crap in the diverter I understand it’s been replaced (if there is crap in the system it’s going to block the inners).

If the pin isn’t coming out enough to make the micro switch I’d check the dhw diaphragm.

What’s the pump proving switch doing?
 
Yeah only thing I can think is more muck has been caught somewhere. Ch works fine.

Inlet filter OK.

Cleaned the plate also.

Was wondering if pcb but I've had to concede defeat. I can't throw any more time/parts at it. Had to be honest with the customer that from a business point of view she is better off getting manufacturer out. Otherwise where do I stop. Not fair on customer to keep returning and I can't spend all day swapping parts.

The fact it worked spot on for a while then started doing the same thing didn't help.

Customer happy with that, I've been honest and not trying to rip them off.
 
There is a venturi for the DHW diaphragm in the right hand brass block. Its the nut below the 2 small copper pipes. The nut is 24mm i think and needs ring spanner to remove. If the venturi fails the microswitch will not make and the diverter will stay in ch mode. This explains all your issues. (as long as the DV is new)
 

Reply to Main combi 24 he hot water issue in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
198
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two...
Replies
2
Views
203
S
Hi, I seemed to have a blockage in kitchen sink. A plumber came and cleared all the pipework that is visible inside my home (there was debris and...
Replies
2
Views
145
Sonya K
S
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
266
PSxxxxxx
P
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
421
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock