L

lambchop

Hi All

Doing a high class B & B (refurb in a listed building) with a dozen bedrooms, disabled public & staff toilet approximately just under 250 loading units (high usage). 42mm copper H & C riser from basement plant room 3 floors and then ending up in attic doing a drop down system to ground floor. All bedrooms are on 1st & 2nd floor.


My concerns are:

Hot return started in 22 mm and dropped to 15mm halfway up riser. Changed this to 22mm, will be putting boiler fixes on some hot returns to stop short circulation and will balance when testing. I know ideally hot return should be teed in at the furthest sanitryware but nature of the building the main branch pipework is well over 3m from the sanitryware. May have to put in another secondary return pump

I have upsized some pipework that were on the plans (eg 2 basins, 1 shower & toilet for 1 bathroom feed by a 22mm and in the same room a bath which had another feed of 22mm from another drop aswell, because of it being listed building could only do one drop so done a 35mm pipe to feed all of this sanitryware) but was this totally necessary if a booster pump and break tank is going to be installed?

I know the men & girls in suits have designed this but as the guy on the ground would appreciate any views, opinions etc I know its fri night and im about to get kicked off the computer, many thanks in advance
 
Status
Not open for further replies.

Reply to Loading units, pipe sizing & booster pump in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, I have just had my central heating system "upgraded" for a four bed-roomed detached house. The heating company recommended going from the open...
Replies
9
Views
1K
Hi Everyone, For those who like a long read but I could rally do with some advice. Might be a bit long this. For background. A...
Replies
3
Views
293
Background I have a small one-bedroom flat in the roof space in a victorian house. There are three floors below and each floor has a single...
Replies
3
Views
604
Hello folks I've moved into a property last month and started to note things that may need looking at. Some of the radiators on the ground floor...
Replies
3
Views
674
I am sizing the central heating pipes for a complete replacement. The property has an elongated floor plan so I have used a piping layout...
Replies
2
Views
1K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock