M

M7R

The last rad in my system, the down stair hall rad, seems to be showing signs of being blocked... but I don't think it is.. heres the info...

The system was installed by the neighbor in the late 60s early 70s, (neighbour still loves next door, they have been in since the house was built in 56!)

it did have a Baxi Bermudia back boiler system, we still have the fire but about 4 years ago while the last owner was in she had a new Vitedons W100 boiler fitted in the bathroom..she had it fitted due to being a pensioner so got it on a grant I believe.. at the same time the boiler was fitted the back boiler was by passed next to the boiler, and the bathroom rad was put on its own loop.

when we moved in 2 years ago I removed all the rads bar the 2 curved ones in the bays (which are going this summer to be replaced by 2 doubles on the other wall as getting 2 curved rads is stupid money!) and replaced them with rads from Wickes, along with adjustable and fixed length adapters to convert the imperial length old rad spacing to slightly smaller metric rads.

I dont know if it has been like this from day one, but certinally for the last 6 months, the hall rad which is the last on the loop and a new rad seems to have the issue of the hot water coming in, going up the first 2 water jackets, and the top being hot, and thats it.. the middle is warm, and the bottom is pretty much room temp, even only 3" from, the inlet!!! (the outlets never red hot either!)

Last weekend I cleaned out the header - see my other post for the mushroom farm I had gown in less than 2 years in there!!! - and filled the system with Sentinal X800 cleaner, which has had a week to work its magic! the rads used to bleed clear, but after I messed around with the system they started to bleed charcoal...emptied, refilled the system and added the x800, and over then today with a mate I dried the system again, wiped down the header (charcoal water but no rust bits etc in there..) and then took off the hall rad, flushed it through with the hose, via the bottom inlets and the top where the blank and vent should be.... when blasting the water through the inlet it came out of the outlet pretty quick, like it was just running along the bottom water way and not up, along the top and back down! it was black-sih for the first few second then charcoal and then clear pretty quick.

we also did the old bay rad before it, got some black water out of it but not masses...

Then we refilled the system with clean water, bleed all the rads, kicked the pump in for 10 mins on high to dilute any crub in the pipes we couldn't get out (with the hall rad locked off to stop any crud going in there)..after 10 mins, drained again, and it was pretty clear really...

then refilled with another shot of X800, the heating has been on for a few hours now, pump on speed 3 as it says and the hall rad is as before, only hot on the top and the first couple of water jackets.. I have been and balanced the system but its made no odds..the old bay rad which is before it red hot top to bottom all the way along, as are the others...

so what do people think? I have even tried hitting the rad at the bottom with a plastic hammer encase there is any crud stuck and the vibration will dis lodge it.. but it doesn't seem to have made any odds...

The rad is a single 1450mm, if that makes and odds, and I am sure it is the last on the loop..

any help of suggestions would be apprecaited, the hall isnt that cold... but it bugs me its not right as all the heat goes straight up the stairs, and I am a bit OCD about things being right..

Cheers

Karl
 
system balanced correctly?

pipework sized correclty?

is it cold in the room?
 
system is balanced the best I can by touch,... but I forgot to say I have turned all the rads off before and its still pretty much the same.

pipe work is the standard 1/2 size

the hall is about 17-18deg, the thermostat is in there, but its a wireless one so can be moved, but the stat is demanding heat when I have been playing with it
 
so if you turn the stat up to 30/max then does the rad get warmer?
 
the rad doesnt have a TRV stat, it has 2 normal values (wide open).

room stat set to 18 or 30 makes no odds, its demanding heat so the boiler is running. the boiler is set to 60deg temp too.
 
id be tempted to change the rad and valves, wont cost much. You may also want to consider a power flush on the system.
 
Valves were new when the rad was installed, they seem to open and close fine... But I am thinking there could be a fault internally in the rad blocking flow along the bottom.... Ill see how the flush goes and may drop another on when we do the other 2, I have been tempted by a power flush but it seems quite expensive... Also when the 2 new rads are installed I will hopefully be adding a magnafilter at the same time
 
does sound like hard sludge in radiator, power flush with a drill vibrator on problem rad would probably clear it but will be expensive, have you tried taking rad off and running garden hose though it, messy but its how we used to do it & does work,
 
you say that you have flushed with hose through vent and cap, this is not not right, take rad off, turn it upside down and flush through where the rad valves connect to rad.

Give the bottom a good hit with the bottom of a hammer/ rubber mallet.

leave flushing for 10-15 minutes, when it runs clear, turn it upside down/ hit it some more, until it is clean.

lift it up so the outlet is at bottom (on step or platform) and flush the rad.

Be careful not to scratch radiator.

This will remove all sludge from radiator.
 
I flushed it through all the inlets and outlets upside down, rights way round... Ill keep the x800 in for a week then take it off and whack it one next weekend, hopefully I can shift what ever is in there, it was running clear today, but I also can't be sure if its been faulty from day one...
 
have you turned all radiators off and left this one on since you flushed it out?
 
Not yet, I planned on doing that tomorrow, but I don't hold out much hope..
 
I would try that, especially with x800 in system, leave it for about an hour.
If that dont work then blockage in pipes.
 
I don't think it is the pipes, as I can shut the inlet and back drain the rad via the return pipe... I had the bleed valve on the inlet side before today and drained about 5l out of it the other day!

also it's odd the way the first 3 ribs in the rad get red hot, then the next is only warm then the rest just Luke warm at best... Pointing to a lack of water flow alsong the main water run along the bottom of the rad... But it appeared to flush fine... Water flowing in and out pretty fast, I would have expected a slower flow rate if the main water passage was blocked.

ill try the 1 rad open tomorrow and report back
 
If it is an old rad and you suspect it is blocked/dirty, then might be worth considering an upgrade to a more modern rad with fins
 
No that's what I'm saying this is a new rad, it's only 2 years old. There only 2 old rads left one up stairs in the front room as its a curved rad in the bay, and the same down stairs, the curved rad is the one before this rad... But logicly that shouldn't make any odds? Unless its higher water content means more water is going into the bay rad then back into the return loop..
 
Definately sounds like a return restriction, you may be able to drain the return feed but that doesn't mean there are no restrictions. Remember each rad is on individual legs and any restriction the majority of heat will take the easy path. I would bet that the restriction is in the pipe and not the rad. You need a proper flush or it may be cheaper in short term to replace the leg. Its my opinion that your wasting your time keep flushing the rad.
 
Okay, power flush it is then once the new rads and pipe work in the bedroom and dining room have been done... I'm lothed to replace that leg of pipe due to the new floor that was laid only a few months ago... Cheers
 
Okay, power flush it is then once the new rads and pipe work in the bedroom and dining room have been done... I'm lothed to replace that leg of pipe due to the new floor that was laid only a few months ago... Cheers

Is there no way to get under the floor?
 
When the heating was installed the neighbour has told me that in the back room there are a few floorboards which are lose, this is where he got in to the crawl space under the house.. The one hall rad is as far away form there as you can get...

but there is news! This morning I have turned off all the rads, turned down the bathroom rad as much as I can without causing the boiler to lock out after a couple of mins, and with the pump on 3 you can hear the water racing through the hall rad! I have left it running for 20 mins while I do other stuff, and now just turned the boiler up to 70deg, gone down stairs and the hall rad is hot top to bottom all the way along.

i am coming to the confusion that the 2 bay rads are robbing too much water, they have to be neary all the way open to get an even heat and they hold a lot of water! I think this is allowing too much water to short circuit back to the boiler before getting to the hall, and that joined with the fact the hall is a big long rad means the water that is making it there is not enough to heat the full rad. However I will leave it running hot with just that one rad open for another hour or so as it won't do any harm to clean those pipes through
 
When you next take the rad off get a bucket and an old washing machine hose. Screw one end of the wash mac hose onto the rad valve and put the other end into the bucket and open up the rad valve. Check to see that the water flows freely into the bucket and this will tell you whether there is any blockages in the pipework feeding the rad.
 
Last edited:
Ok will do next weekend when we whip it off again, it seems to be flowing really well now though all the others are turned off,
 
Tolly gives good advice there mate, i would expect the rad to have flowed as only route now it does sound though that your bay window rads need restricting
 
Sounds like a circulation problem to me not the rads as it's hot hot all over when uve shut everything off
Check if a bypass is fitted and ensure its not fully open, does the problem occur all the time or just when heat and hw on? If this is the case a balancing valid on hw rtn maybe req, do u have a combined air/dirt separator for the cold feed and vent cos I've know them to get blocked, check the pump, if the systems old it can block/restrict the unions on the pump but the pump appears fine.
Hope this helps but definitely sounds like a circulation/balancing issue not the rad
 
The pump is as old as the boiler, I have stripped and cleaned it as it got blocked on the last clean due to the crap x800 which had been frozen... Cleaned and cleaned the system, all is good. The pipe work Round the boiler and pump is new too as it was all changed when the boiler was added.

hw balance is only 1 and a bit turns open, but the problem is the same even when he is not demanding heat and the valve closed.

i have balance the system again and the problem is back, I'm sure the bays are t helping, as they have old valves where it's only one turn from closed to open, both are set about 1/2 open or just under, this is where the inlet is very hot and the outlet is just warm to hot.. So a out right, the rest of the rads are about the same with the valves being new and about 1 to 2 turns open apart from the hall which is wide open.
 
How bout the bypass it's btwn the pump and the 2/3ports and goes straight to the rtn, and if this is too open it'll short circuit back to the boiler
 
Also check the cold feed/vent arrangement, if uve got a combined one its possible it's blocked. Where's the hall rad that's fully open in relation to the one that's not working, and waters lazy an it'll take the easiest path.
Just to confirm if the other rads are off the problem rad is hot all over?
Still sounds like a circulation fault tho
 
I have a separate vent and feed, when we drained and refilled the system the vent was gurgling and spitting water every so often so I know that's clear.

the problem rad is the hall one, is the last on the loop and a 1.4m single, which comes after the 1.4 old rad in the dining room bay, a big old rad with out fins, -this is being replaced in a couple of months, along with the old bay rad in our bedroom.

if its still a prob after the other 2 old rads have been replaced then ill be annoyed..
 
Have you considered pressurising the system, that bit of extra pressure might help the flow a bit.
 
A Friend of mine recently had a problem with his boiler over pressurising due to a failed part, he was convinced he could fix without replacing the part. He drained down and flushed his system numerous times and was convinced the system is clean. He has disturbed debri in the return leg from a rad and now has similar to yourself.
From everything you have written i still believe you need to powerflush the system and balance correctly as you have indicated all rads are currently set the same.
 
I thought of that but was advised against it due to some bits of the system being 40 years old, there was a higher risk of leaks, and little to gain really.
 
There is obviously a risk but more often than not it only ever helps and is normally pretty straight forward to achieve. Make sure your boiler has an overheat stat on it though.
 
I haven't seen any of the pipe work as it is all under the floor boards, I will ask next door next time I see him in the week, see if he remembers how he imbed t all in, but I doubt there is a by pass
 
Status
Not open for further replies.

Reply to Last rad cold at the bottom - bit of an odd one as I don't think its blocked... in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi - I'm a reasonably experienced DIY plumber but just can't work out why the last new rad I've installed is cold - would really appreciate your help please. I've extended an existing 'run' of radiators - the last one on the run ( in downstairs kitchen) is cold. The first rad added is...
Replies
7
Views
638
Hoping somebody can help, So, in a nutshell… Standard 90s Westbury home – condensing boiler, pump, wall thermostat, etc etc... Normal, common or garden, run-of-the-mill British housing estate CH setup. Downstairs radiator, 1 of 2 in our living room, went cold one evening mid-November last...
Replies
8
Views
558
Hi all, Got a nightmare situation with a central heating system I recently adopted. It's an open vent system with a combined F&E pipe, with a Worcester greenstar danesmoor 18/25 oil boiler. Covers 10 radiators mostly large double panels, some towel rails and smaller rads too, as well as an...
Replies
17
Views
2K
… praying to the plumbing God, Bob Pictures and layout details attached, so be patient. 21 year old oil fired system in pretty good nick. I noticed some minor pumping over from the vent (occasional burst of water, and the odd dribble). Didn’t think much of it as I was about to replace the...
Replies
7
Views
1K
Hello. I've just replaced our old Potterton EP2 CH controller with a Drayton Wiser HubR (& peripherals). The old backing plate wasn't compatible with the new universal one, but the wiring was pretty close AFAICT (N, L, 1, 3 & 4 connected) .When I first powered it up but didn't have any TRVs...
Replies
1
Views
264
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock