Ryster

Second post in as many days.
Just been in plumb centre and was earwigging on two guys talking about testing.
Now I'm a commercial fitter with domestic as well. Granted I have not used my domestic that much over the years but it does get used.

Now the way I was taught was the following;

Upon entering a building to do gas work you do the following:
1 minute let-by at 10mbar
1 minute stabilisation at 20mbar keeping at 20 for that minute
2 minutes at 20mbar.
Anything above 75mbar is medium pressure and requires a different test (this was where I got into conversation with them as they said anything over 82.5 was medium)

Any Drops at stabilisation are fine, any drops within 2 minute test need to be within permitted limit otherwise test fail and you need to find the source

You then do any work IE boiler service, then after the work do the same again.

Now these two guys argued with me for five minutes that you do only need to do a 2 minute test at 20mbar.
Any drop is fine as long as there is no smell of gas.
Also that doing a test upon entry is not needed, and I was wasting my time.

Now somebody please tell me I'm right, I don't have my domestic viper with Me so cannot check, but I will be mortified if I have been doing it wrong all these years!

Honestly these lads have put complete doubt in my mind now, to the point that I'm worried about doing a test today!
 
you must perform a tightness before touching any part of the gas installation to make sure you have not caused a leak yourself. for example you test and find a 2mb drop, then carry out your work, test again and you have a 3mb drop. Something you have done may have caused the extra drop and will need checking.

If you dont perform the first test then you cant be sure of your own work being correct, and also if you dont test first and it has a drop outside the allowable limits then you will be responsible for finding the problem im my eyes.

It takes 3-4 mins to do a correct tightness test, i cant see what you will save by not doing one?
 
any drop isnt fine even if you cant smell it, on pipework.. appliances depends on the meter
 
So i was right then.

I hate ****s like this, they were so cock sure about what they were doing it put doubt in my mind about the process I use.
 
Sound like the sort of tossers I used to see in Plumb Centers all the time before I stopped using em; Snickers work trousers (Regulation bright blue), Walk straight round counter like they own the place and get their gear from the back themselves, rest beer gut on counter while drinking free coffee and telling everyone that will listen that "They're pulled out with work, aint had a day off since 1976, fitted 2 full systems since 8 this morning and still got another 3 to fit before 4 o clock & I don't need to do a tightness test cos I'm the bestest fastest gas fitter in (Insert the town/city of your choice)!" I always do a test before and after every job cos to be honest, I'm just too pretty to go to prison:cool:
These sort of blokes can make you doubt yourself and love to think they look big in the merchants. Rant over!!:mad:
 
I don't do an additional stabilisation period at 20mbar.The let-by test at 10mbar also acts as a stabilisation period.

It's not mandatory to do a tightness test on a service either.
 
I hate guys like that who make you doubt your own best judgement, just because they are so full of themselfs and manipulative, I was working in my mates house fixing his shower and his step dad was trying to give me advice then saying what i done was wrong, me scratching my head trying to figure out what for 10 mins then realised i was right ! wish he just kept out my way !

But a normal test is 1 minute let by, 1 minute stabilisation if it drops bellow 20mb put it back up to 20mb for 2 mins tightness, if there is a drop which is in tolerance of the meter during the tightness test then it should be fine unless there is a smell of gas. Although you only do a tightness test if you are working on any gas pipework, I don't think one is needed for a boiler service I would do a mini tightness test if I was working on a boiler sometimes where you isolate the gas supply to the boiler and check for tightness from P1
 
Last edited:
It's not mandatory unless you touch the gas. I do one for my own peace of mind and have actually found a couple of leaks that the customers didn't know about elsewhere in the property. I you do a service and a customer reports a smell of gas afterwards, the finger will automatically point at you, then you've got all the hassle that comes with that, all for the sake of 4 minutes. Do it by the book and no-one can argue!
 
did you give there horses out the front any water, its pretty warm today, actually I think I can hear their stirrups clinking in the distance, hope their not working round here.

Just checked my viper and Medium Pressure Installations are max 2bar and min 75mbar
 
Tell the morons to come on here later for some discussions ! Agreed with above times and tests. I always do my tests before i touch any gas appliances or pipework.
 
Sound like the sort of tossers I used to see in Plumb Centers all the time before I stopped using em; Snickers work trousers (Regulation bright blue), Walk straight round counter like they own the place and get their gear from the back themselves, rest beer gut on counter while drinking free coffee and telling everyone that will listen that "They're pulled out with work, aint had a day off since 1976, fitted 2 full systems since 8 this morning and still got another 3 to fit before 4 o clock & I don't need to do a tightness test cos I'm the bestest fastest gas fitter in (Insert the town/city of your choice)!" I always do a test before and after every job cos to be honest, I'm just too pretty to go to prison:cool:
These sort of blokes can make you doubt yourself and love to think they look big in the merchants. Rant over!!:mad:

you know the guy that trained me then, this is a copy to how i would describe him.
taught me to do a let-by at 6mb, went into the center with this and i didnt know which way to turn.git.
 
You dont have to do a tightness test if you are just servicing the boiler and you can isolate the gas at the appliance.
 
Well,at the risk of playing Devils' Advocate technically these guys were right.

The actual test period is 2 minutes,and you don't have to do a tightness test if you're doing routine maintenance on an appliance. So going by the information in the original post it seems to be factually correct.Whether it's bad practice or not is another matter however.
 
A tightness test should always be done before you start working.
untitled.JPG

Anyone who doesn't is not only stupid but also incompetent.

Low pressure is up to 75mb, medium pressure 75mb - 2 bar.
This pressure relates to the incoming service and the outlet pressure (domestic) will be the same regardless (some i&c stuff will be higher) and slightly different test methods are used but the same principles apply.

Even if you don't do a tightness test on a service if you are isolating it at the valve, any broken joints still need testing with soapy.
 
I think i'll continue to do a test before and after every job, when all's said and done it takes minutes.
 
do you think its wise to do one though?

If a customer complains of a smell of gas or asks me to test it, I will. For just a service on an appliance with an isolation valve there is no need to, thats the way I have been shown and taught. As tamz said, any disturbed joints I always soap up or if hard to get to with LDF use my gas sniffer.
 
if your going to meter to do gas rate or working pressures then i cant see any reason not to perform a tightness test on any type of work, if you find a problem then you may gain extra work too. ;)
 
you must perform a tightness before touching any part of the gas installation to make sure you have not caused a leak yourself. for example you test and find a 2mb drop, then carry out your work, test again and you have a 3mb drop. Something you have done may have caused the extra drop and will need checking.

If you dont perform the first test then you cant be sure of your own work being correct, and also if you dont test first and it has a drop outside the allowable limits then you will be responsible for finding the problem im my eyes.

It takes 3-4 mins to do a correct tightness test, i cant see what you will save by not doing one?

can you clarify what you mean by the bit i have highlighted, if taken literally as ANY work needs a TT then you are wrong, you do not NEED to do a TT when you service or repair a gas appliance for a private customer (by that i mean not a tenanted property) if you mean before altering or adding to a carcass then i agree with you
 
i have this discussion almost weekly in the training centre, some disagree when i say you dont need to do one for every task, they say yes you should and they do as they like to sleep at night, my answer to that is "so you do a TT when not mandatory and find a 2mb leak, do you then isolate appliances and test carcass only or are you happy to leave 2mb" some say they leave it but if they want to sleep well at night how can they leave a 2mb drop which might be on a pipe, which we all know cant be left, they are doing half a task rather than completing the whole thing, so either comply with the reg or go the whole hog and if you overstep the reg then do everything that you can to determine where the 2mb drop is, or do what i do any fully comply with the reg and test when mandatory (as long as you know when it is mandatory, and i do)
 
can you clarify what you mean by the bit i have highlighted, if taken literally as ANY work needs a TT then you are wrong, you do not NEED to do a TT when you service or repair a gas appliance for a private customer (by that i mean not a tenanted property) if you mean before altering or adding to a carcass then i agree with you

i was talking about installation/work on pipework, i guess it could have been worded better ;). I perform a tightness test no matter what work i am doing as thats the way i have always done things, working 17 years in tennanted housing gets you into the habbit!
 
i was talking about installation/work on pipework, i guess it could have been worded better ;). I perform a tightness test no matter what work i am doing as thats the way i have always done things, working 17 years in tennanted housing gets you into the habbit!
You only need to do it after but common sense suggests doing it before can be a good idea to protect yourself against being blamed for problems already there. Question is in you long years of experence how useful has it to you to do a TT before?
You can find the requirements under technical guidence when you log into GSR - search tightness.

I am not sure Kirkgas is right or wrong about servicing and repairing. I think you DO need to do a TT AFTER certain types of repair. You guys check the technical guidence.
 
Last edited by a moderator:
how useful? very.

Number of times i have entered a property and found a problem, pointless adding a new appliance onto an exsisting carcus if it needs repair/replacing. Some Landlords are crafty and try to make it your problem once you have started work.

always protect yourself i say!
 
Last edited:
i have also worked for landlords that require the recording of the results of your initial and final tightness tests on your landlord cert, something they insisted on.
 
i have this discussion almost weekly in the training centre, some disagree when i say you dont need to do one for every task, they say yes you should and they do as they like to sleep at night, my answer to that is "so you do a TT when not mandatory and find a 2mb leak, do you then isolate appliances and test carcass only or are you happy to leave 2mb" some say they leave it but if they want to sleep well at night how can they leave a 2mb drop which might be on a pipe, which we all know cant be left, they are doing half a task rather than completing the whole thing, so either comply with the reg or go the whole hog and if you overstep the reg then do everything that you can to determine where the 2mb drop is, or do what i do any fully comply with the reg and test when mandatory (as long as you know when it is mandatory, and i do)


I was waiting for you to come along and answer on this lol. My exact feelings on it. You are opening a can of worms and will end up with an unhappy customer.
 
It is good practice to carry out a tightness test during a routine service, although not mandatory.
A tightness test is only required during a routine service if you have to interrupt the gas supply to an installation. ie. removing an appliance etc. or if you suspect a gas leak.

As most of us know, BG do not want the headache of investigating permissible drops in install after install so they do not carry out a tightness test as a mater of course.
 
its not mandatory, so to hell with it.. if their is a massive leak under the floor, just leave it till something goes bang?...

if you find a leak doing a TT even though you didnt really have to, i'd have thought most people would be happy, most normal people wouldnt want a gas leak.. if people are testing but then leaving the problem, thats their problem, if they're happy to assume its not a danger to life
 
You only need to do it after but common sense suggests doing it before can be a good idea to protect yourself against being blamed for problems already there. Question is in you long years of experence how useful has it to you to do a TT before?
You can find the requirements under technical guidence when you log into GSR - search tightness.

I am not sure Kirkgas is right or wrong about servicing and repairing. I think you DO need to do a TT. You guys check the technical guidence.

Kirkgas is spot on.

Doing a TT before a job is a requirement not just common sense before carrying out installation/alteration to pipework.
Servicing, only broken joints need checking if issolated at appliance.
If no issolation at appliance you must do the TT's when you turn off at meter.

If you do, do TT's on every job for peace of mind the full criteria must be carried out.
 
if you had to do a tightness test on each appliance you work on, then why the need for service/isolation valves? Test for tightness at P1 and spray with LDF no need to do full carcass unless alteration to pipework, write what you done on paperwork
 
You only need to do it after but common sense suggests doing it before can be a good idea to protect yourself against being blamed for problems already there. Question is in you long years of experence how useful has it to you to do a TT before?
You can find the requirements under technical guidence when you log into GSR - search tightness.

I am not sure Kirkgas is right or wrong about servicing and repairing. I think you DO need to do a TT. You guys check the technical guidence.


you are wrong with both the highlighted comments:p
if you NEED to do a TT then only doing it after can prove problematic, ie if you alter a pipe and do a TT after and find no drop then all is well (and you are lucky) but if you alter the pipe, test after and find a 1mb drop then you cannot CONFIRM that the drop isnt on your new work, the amount of muppets who i have to keep right on this is terrible, they say as long as you do a TT after the install and it is under permissable drop then you are fine,
the second point is not open for discussion there is MY way and the WRONG way:cool:, seriously, if you think i'm wrong then you need to check the technical guidence, apologies may be written on the back of a £5 note
 
I was waiting for you to come along and answer on this lol. My exact feelings on it. You are opening a can of worms and will end up with an unhappy customer.


haha at least i'm dependable
 
if you had to do a tightness test on each appliance you work on, then why the need for service/isolation valves? Test for tightness at P1 and spray with LDF no need to do full carcass unless alteration to pipework, write what you done on paperwork
Yes that is right.

Mr TP is home and he can't believe such heated debate among all you Gas Qualified engineers!

There is nothing wrong with doing TT before any work, I said I think it might be a good idea and I asked whether you had found this useful.

According to the Rules, however, eg: on GSR technical guidence website, it is NOT compulsory to do a TT before any gas work.
Kirkgas, what you are saying makes sense but the question is about what what are the rules.

MR TP tells me you should do a TT before anything else IF the customer smells gas.
Like Kirk gas he would do a TT before any alteration of the gas carcus eg installation of new appliance, because AFTER any alteration to the gas Carcus NO DROP is permissible.

Kirkgas this is what you said and you are right.
There is no permissible drop after installation of boilers or other pipework alterations.

As for after servicing no TT OK.
Anything else:
The Gas Safety (Installation and Use) Regulations 1998
6 (6) Where a person carries out any work in relation to a gas fitting which might affect the gas tightness of the gas installation he shall immediately thereafter test the installation for gas tightness at least as far as the nearest valves upstream and downstream in the installation.
There i s more explanation of this at GSR website, when you login as installer.
 
Status
Not open for further replies.

Reply to Just had an argument about tightness testing in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

My son has an apprenticeship interview for to become a plumber and heating engineer. The have said there will be a multiple choice exam for this for suitability. The thing is my son panics during tests/exams. Is there any book I can buy him to practice the multiple choice test for the exam? What...
Replies
3
Views
428
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
353
Hello all, I'm would like to extend an existing outside tap to another point in the garden. I'm about to pour a concrete patio and was hoping to run the water line underneath. There are existing drain (and who knows what) pipes running along the same wall so I'm nervous about digging too far...
Replies
6
Views
240
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
253
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
275
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock