sasik

The boiler work for about 30 sec and then stop, 30sec later it will come on again and so on. The boiler working like this for the last two days.
The problem occured when the system demand for heating and hot water.

What could be the problem?
 
I've found this problem before, it wore out the gas valve soleniod. I found an resetable over heat stat was cuasing the problem.
Try replacing, relatively inexspensive.

Regards Andy
 
The radiators are ok, but the water in the cylinder are only warm!
 
Have you checked cylinder stat?
Do you have a 3 port or 2x2 port moterised valves?

If 2 port valve on HW lock open valve (if possible) when calling for heat, does cylinder flow and return get hot?

Do you have any way of venting cylinder coil? (sometimes air becomes trapped reducing flow)

If venting the cylinder fails, possible component faillure or wiring fault.

Regards Andy
 
Last edited by a moderator:
Hi Andrew

At first I thought the problem was with the hot water only, but I have the same problem when the heating system is on demanding (boiler run for 30sec then off for 30sec...)
So I don't know if I have a problem with the boiler or with one of the components around the hot water cylinder.
 
Status
Not open for further replies.

Reply to Ideal Elan 2 boiler fault! in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
150
Hi, I have a Worcester 28i junior boiler that has started to lose pressure, only when using the central heating. When using hot water I have no issue, however, when running the heating the pressure drops. Im looking for some ideas on what could be causing this. I have no sign of pipe leaks...
Replies
6
Views
205
Hi, Later this year I am going away for a 2 week holiday and as the weather will be warm there is no need for the heating to be on and arguably no need for me to needlessly heat hot water. My intention was to turn the boiler off along with the mains water when going away. Now, I have heard...
Replies
1
Views
108
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
311
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
231
P
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock