I'm really grateful of the support. Here is the full details of the current rads. The lounge as you can probably guess is where the two Double Plus (or K2 I believe) are. I presume you would have to upgrade all the radiators to keep the system design balanced? So this would mean larger physical radiators in the lounge? I guess I should have done my research better regarding the minimum output rate of the boiler, I went with the Ideal ones as they were a heat only boiler that did support DHWP with Opentherm. Not sure other / better choice there was given the system as is? I guess I should just be greatful that I'm in a well insulated house that doesn't need much energy to keep warm.
Radiators.png
 
There must be someway of limiting the minimum flow temperature surely to say 48/50ish to get the boiler away?, also maybe ask Ideal if there is some method of extending the anticycle time, if required.
What is the flow temperature on DHWP and does the boiler cycle when the cylinder temperature nears its SP of 60C?.
 
Hi John, yes I think you are spot on, if the minimum set flow temperature was around 50 degrees the boiler wouldn't overshoot. The room temperature would just be reached a bit sooner and the boiler would just be told to turn off in my case for probably around 30mins. This would be far preferable to the short cycling and longer time to get to room temperature. I've pinged an email off to Rishi Chandra to request the option. Will be interesting to see if I get a reply. The NEST Gen 3 is an old product now and I suspect the dev team have long since moved on to something else. I have been researching Opentherm gateways to act an intelligent middleman but I'd really rather not have some Heath Robinson contraption in the system.
 

Reply to Ideal boiler cycling with Nest & Opentherm in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar plumbing topics

    • Like
Hi everyone, Just wanted to share my experience with "upgrading" an S plan setup to Opentherm and Vaillant Control Center (VR66). There are a few...
Replies
1
Views
1K
Hi Folks, I have a challenge with a Main Eco Elite 30 Combi which is short cycling on the CH. Water works fine. As soon as you have call for...
Replies
6
Views
426
My heating system comprises an Ideal Logic 12 boiler located downstairs and a Gledhill OV SOL cylinder located upstairs . The problem is that when...
Replies
1
Views
500
B
Issue with boiler short cycling in system with hot water tank. We have an ideal heating logic heat2 h15 boiler which feeds a hot water tank...
Replies
10
Views
1K
I have a home with an oil boiler in a garage turned into a flat, heating both flat and main house, running c plan with two pumps, two motorised...
Replies
0
Views
408
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock