There for limiting water flow eg cold and hot

Won’t be any good on heating and will short circuit as always open
 
Yes but the "wondervalve" above claims that it will (or might) maintain a fixed flow with a varying pump head as will occur with PP operation. The setter valve is recommended for a pump on a CP (constant pressure) setting but the flow would vary in pump PP mode?.
 
Grundfos's note (attached) on their newish Alpha2 pumps and ABVs in CP and PP modes is worth a look. The parting comment there (for PP mode) is that "If an automatic bypass valve must be used, then a manual fixed bypass valve should be installed in series with the automatic bypass valve. The fixed manual bypass will restrict the flow as the automatic bypass valve opens."
 

Attachments

  • Grundfos Alpha2 and ABVs.pdf
    167.4 KB · Views: 57
Grundfos's note (attached) on their newish Alpha2 pumps and ABVs in CP and PP modes is worth a look. The parting comment there (for PP mode) is that "If an automatic bypass valve must be used, then a manual fixed bypass valve should be installed in series with the automatic bypass valve. The fixed manual bypass will restrict the flow as the automatic bypass valve opens."

I don't see any advantage in having a ABV+fixed bypass over a fixed bypass alone. See my post #10.
The wondervalve may improve this again, it will be interesting when/if they reply to your email.
 
Agreed - I found their argument a bit strange. It appears that the only circumstance where a differential pressure driven ABV would be effective is where the pump has a monotonically decreasing head from zero flow onwards. And none of Grundfos's domestic pumps have this as far as I know.
 

Reply to Honeywell ABV setting in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler pump menu for either 70% or 100%, so, is the pump set at either one of two fixed speed percentages or does the pump actually vary speed, (modulate)...
Replies
1
Views
147
Hi all. Hope you have all been keeping well. A while back I decided I only wanted to fit one brand of boiler and decided on Viessmann due to space for servicing and changing parts if ever needing to. I am finding my decision rather hard due to the different clearances on flue runs and cupboards...
Replies
9
Views
213
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
478
Hello all, I'm would like to extend an existing outside tap to another point in the garden. I'm about to pour a concrete patio and was hoping to run the water line underneath. There are existing drain (and who knows what) pipes running along the same wall so I'm nervous about digging too far...
Replies
6
Views
231
S
Hi, I seemed to have a blockage in kitchen sink. A plumber came and cleared all the pipework that is visible inside my home (there was debris and pebbles!) We saw that the pipe that takes water down the gutter was visibly full to the top. He said he will return with a coil to push through...
Replies
1
Views
65
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock