Hi was just looking a second opinion on a job ive to look at. Its a old grant 50/70 euroflame. Its on an open vent system with no stats inside house. The high limit stat trips most days not while its in its cycle . Im told it wotks ok then just trips out after it switches off at time clock. I know it cud be poor circulation or pump but im thinking the stat with the way its going. Thanks in advance .
 
Pump stops when boiler switches off so there is no circulation but the latent heat builds up another few degrees.
Change the overheat stat.
 
Ye as far as i know eveything works fine until it switches off at timeclock then u nearly always have to hit the high limit. To be honest he knows nothing at all about it so he has trouble explaining it well..
 
Heat does build up. Main control stat might be turned up full or else it might be faulty & not the limit stat which is perhaps just doing its job correctly
 
As Best says..would change boiler thermostat first as maybe existing out of calibration..maybe fit pump over run if problem persists just for fun and show custurd how clever you are..always good to impress
:sorcerer:
 
Status
Not open for further replies.

Reply to high limit stat in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Am trying to understand my mother's Apollo boiler. It has an intermittent fault. In the last couple of years, it has had a new...
Replies
4
Views
859
Can anyone help, please? I'm looking for a heating system circulation pump for a domestic install, with 3 speeds, where the speed can be toggled...
Replies
6
Views
1K
Hope someone can suggest where I should looking to resolve this one... I have a Bosch 30Cdi regular boiler on an S plan system with a 180L...
Replies
12
Views
4K
Hi there, thanks for your time to look at this record long post!! I work on the operational management side or a small building contracting firm...
Replies
9
Views
1K
H
Hi there, thanks for your time to look at this record long post!! I work on the operational management side or a small building contracting firm...
Replies
0
Views
657
HRP123
H
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock