Hi

Not sure if anyone can give any ideas - but
I’ve got a Worcester Bosch junior 24i system boiler.

For the past 10 years I’ve lived In the house - the average usage of gas has been about 10,000kwh. For the past 2 years my average has been 58000kwh. (Boiler is the only gas appliance in the house!)

It’s Regularly serviced. And from the 3 plumbers I’ve had look at it - they’ve all said - it’s just colder than normal so usage has gone up!

Anyone got any ideas? Is that an increase others are seeing?

SG
 
You are either using it a lot more than before or there is a problem with the meter or you have a gas leak. How long is heating on for is it a combi or do you have a cylinder
 
Hi!

we’ve always had tado installed

It’s a system boiler with unvented cylinder

When we were away, I turned everything off - and gas usage was 0 - which I presume pretty much rules out a leak?

Is there any way to prove the gas meter theory?

Steve
 
Hi!

we’ve always had tado installed

It’s a system boiler with unvented cylinder

When we were away, I turned everything off - and gas usage was 0 - which I presume pretty much rules out a leak?

Is there any way to prove the gas meter theory?

Steve
Other than having it tested, by gas supplier not sure
 
Yes also seen them when they don’t register how is the meter record (for billing) inputted eg do you do it online or does your supplier
 
Hi!

we’ve always had tado installed

It’s a system boiler with unvented cylinder

When we were away, I turned everything off - and gas usage was 0 - which I presume pretty much rules out a leak?

Is there any way to prove the gas meter theory?

Steve
580000kwh/annum = 159kwh/day, doesn't make any sense as this is the winter/summer average.
Can you see the units/decimal places on your meter, depending on what you find, if you can then get your boiler to fire flat out (24kw) for say 5 or even 2 minutes then will soon see if a meter problem.
 
I think your Worcester bosch junior 24i system boiler is not getting the proper gas supply that's why your boiler not working properly. The heating output is 24Kw is ideal for any property with around 15 radiators.

Please share the pics so that I can help you more efficiently. If your boiler comes under the brand warranty then please contact customer care.

The second option will be you can take advice from the professional rooter and plumbing service provider near your area. Because the boiler system needs an engineer to fix it.
 
The boiler is no longer under warranty sadly

We’ve had a number of gas safe engineers to check and service it - so I’d hope they would have confirmed the gas? Would that be part of a service?

What should I take pics of?
 
If the usage is actually ~ 10,000kwh/annum and not 58,000kwh/annum and if a boiler problem then it must be running at around 15% efficiency, (10/58*85%), scarcely believable?, the easiest/obvious first port of call IMO is to monitor the meter readings over a few minutes while running the boiler at its 24kw output.
 
The boiler is no longer under warranty sadly

We’ve had a number of gas safe engineers to check and service it - so I’d hope they would have confirmed the gas? Would that be part of a service?

What should I take pics of?
Can you (also) post a photo of your gas meter.
 
If the usage is actually ~ 10,000kwh/annum and not 58,000kwh/annum and if a boiler problem then it must be running at around 15% efficiency, (10/58*85%), scarcely believable?, the easiest/obvious first port of call IMO is to monitor the meter readings over a few minutes while running the boiler at its 24kw output.
It’s been about 58000/annum for the past 2 years!

I presume I put it in service mode to make sure it’s running full steam? And then monitor the gas meter for the time?

Thank you!
 
If service mode means that it opens all zone valves etc and then fires at 100%, then, yes, if not just turn up the room thermostats and the cylinder stats and ensure all zones calling for heat, then monitor gas usage for exactly two minutes or so, your meter must show decimal point measurement, if not it may have a flashing LED which may be used to monitor like our smart elect meters.

If a combi boiler just open all hot taps & showers.
 

Attachments

  • E960869D-59FC-4FD6-83A4-46B3635AAC3A.jpeg
    E960869D-59FC-4FD6-83A4-46B3635AAC3A.jpeg
    462.5 KB · Views: 24
If service mode means that it opens all zone valves etc and then fires at 100%, then, yes, if not just turn up the room thermostats and the cylinder stats and ensure all zones calling for heat, then monitor gas usage for exactly two minutes or so, your meter must show decimal point measurement, if not it may have a flashing LED which may be used to monitor like our smart elect meters.

If a combi boiler just open all hot taps & showers.
So I just did the test - put the boiler in service mode - turned the radiators all on (tado) and then watched the meter for 2 minutes exactly

The reading started at 4559.622 m3 and then went to 4559.672 m3 at the end of the 2 mins.
 
Last edited:
I think you miss typed ? Either the first or last figure 3rd number in ?
 
That's a consumption of 0.050M3/2min, = 0.050*60/2, 1.5M3/hr, = 1.5*10.8, 16.2kwh = ~ 16.2*85%, 13.8kw boiler output.
That's probably OK as the boiler would not be firing full out to service rads only, So IMO, beyond any reasonable doubt, the meter is reading correctly.
Would suggest monitoring the meter reading over say exactly two full days and see what you consume, to convert..... Kwh = M3X10.8. To annualize it, Kwh = M3X10.8X365/2. (or divide by whatever the monitored period was).Depending on what you get then you must decide your course of action.
 
That's a consumption of 0.050M3/2min, = 0.050*60/2, 1.5M3/hr, = 1.5*10.8, 16.2kwh = ~ 16.2*85%, 13.8kw boiler output.
That's probably OK as the boiler would not be firing full out to service rads only, So IMO, beyond any reasonable doubt, the meter is reading correctly.
Would suggest monitoring the meter reading over say exactly two full days and see what you consume, to convert..... Kwh = M3X10.8. To annualize it, Kwh = M3X10.8X365/2. (or divide by whatever the monitored period was).Depending on what you get then you must decide your course of action.
Thanks for the calculations! I’ll monitor for a few days then report back on the readings.

On the basis the readings are right - it would seem that the boiler must be firing most of the time to use that amount of gas? If so - what are the potential causes that it’s not getting the house to temperature quick enough?

The tado appears to be working - as I’ve stood by the boiler and amended the temperature and the boiler responded accordingly.

Could the pump not be sending the hot water round fast enough? A blockage? Faulty valve somewhere sending the hot water though?
 
Might have got up too early but where's the problem? both are the same, so 4559.672-4559.622 = 0.05M3/2min.
The reading started at 4559.622 m3 and then went to 4559.672 m3 at the end of the 2 mins. Post #16
Apologies - 4559.622 and 4559.672 Post#18
 
Might have got up too early but where's the problem? both are the same, so 4559.672-4559.622 = 0.05M3/2min.
The reading started at 4559.622 m3 and then went to 4559.672 m3 at the end of the 2 mins. Post #16
Apologies - 4559.622 and 4559.672 Post#18
I amended It in the original post to save confusion - seems it did the opposite! Sorry
 
Thanks for the calculations! I’ll monitor for a few days then report back on the readings.

On the basis the readings are right - it would seem that the boiler must be firing most of the time to use that amount of gas? If so - what are the potential causes that it’s not getting the house to temperature quick enough?

The tado appears to be working - as I’ve stood by the boiler and amended the temperature and the boiler responded accordingly.

Could the pump not be sending the hot water round fast enough? A blockage? Faulty valve somewhere sending the hot water though?
Can't say from that meter check reading what your "normal" daily consumption but once your house is up to temp then would expect something like say a boiler output of 3 to 5 kw to maintain that temperature, so maybe monitor it every hour or so as well, and post back.
 
Can't say from that meter check reading what your "normal" daily consumption but once your house is up to temp then would expect something like say a boiler output of 3 to 5 kw to maintain that temperature, so maybe monitor it every hour or so as well, and post back.
After 2 hours, the reading was 4562.288

So its used 2.616m3 in 2 hours
 
The new meter has clocked up 4560 m^3 since 07-Sep-2020. That's a total of ca 10.8 kW hr m^{-3} * 4560 m^3 = 49,250 kW hr over 16 months, which I make 37,000 kW hr / yr. This includes one summer and 1.5 winter seasons so your annual consumpt is more like 30,000 kW hr, roughly half the 58,000 kW hr quoted in post #1. Hence, I think that the 58,000 kW hr must be the total for two years, i.e. 29,000 kW hr.

If I'm right, we're looking for a way to explain an extra 19,000 kW hr per annum, i.e. 52 kW hr / day, or the equivalent of 2 kW continuous loss.

The easiest way to waste this amount of heat without really noticing is to have a hot water leak. This would be quite significant, I make it about 0.62 litre per minute.

Anyway, try comparing the consumption with the cold feed to the hot water cylinder off vs on. Do you have any unbalanced mixer taps/showers? Any applicances fed with hot water? If you look at your water meter, is there an unexplained 0.62 litre per minute of consumption? Did your water consumption jump (by ca 320 m^3 per annum!) at the same time as your gas bill?

(Someone should check my figures and reasoning, I'm pressed for time right now so the above was a bit rushed.)
 
Last edited:
That seems quite high IMO, its a boiler output of 12kw, would have expected around 50% of this.
Is this whole house heating or just one zone like downstairs, room stat setting also affects usage, I average 4 to 5kwh with downstairs at 20C and upstairs at 16/18C for 16 hours/day, oil firing, 50 year old house.
Have you any bills (personal details redacted) for any summer periods, like the past summer and any summer when the consumption averaged 10,000kwh/annum and ditto for any winter periods?.
Is there very high HW usage like teens continuously showering?.
 
The new meter has clocked up 4560 m^3 since 07-Sep-2020. That's a total of ca 10.8 kW hr m^{-3} * 4560 m^3 = 49,250 kW hr over 16 months, which I make 37,000 kW hr / yr. This includes one summer and 1.5 winter seasons so your annual consumpt is more like 30,000 kW hr, roughly half the 58,000 kW hr quoted in post #1. Hence, I think that the 58,000 kW hr must be the total for two years, i.e. 29,000 kW hr.

If I'm right, we're looking for a way to explain an extra 19,000 kW hr per annum, i.e. 52 kW hr / day, or the equivalent of 2 kW continuous loss.

The easiest way to waste this amount of heat without really noticing is to have a hot water leak. This would be quite significant, I make it about 0.62 litre per minute.

Anyway, try comparing the consumption with the cold feed to the hot water cylinder off vs on. Do you have any unbalanced mixer taps/showers? Any applicances fed with hot water? If you look at your water meter, is there an unexplained 0.62 litre per minute of consumption? Did your water consumption jump (by ca 320 m^3 per annum!) at the same time as your gas bill?

(Someone should check my figures and reasoning, I'm pressed for time right now so the above was a bit rushed.)
Rushed or not, you are right on the ball, annualizing the new meter its ~ 33,231kwh/annum or 91kwh/day, 10,000kwh/annum = 27.4kwh/day, shortfall 64kwh/day. if HW leak then 0.76LPM or 400M3/annum.

So suggest shutting off cold feed to HW cylinder and take another set of hourly readings.
Is the HW cylinder heating controlled by programmer and cylinder stat?.
 
ok, so here is a bill from May/June last year when the heating was off. Water was on constant as it always is (Notice the estimation on the right)


1642074344866.png

Rushed or not, you are right on the ball, annualizing the new meter its ~ 33,231kwh/annum or 91kwh/day, 10,000kwh/annum = 27.4kwh/day, shortfall 64kwh/day. if HW leak then 0.76LPM or 400M3/annum.

So suggest shutting off cold feed to HW cylinder and take another set of hourly readings.
Is the HW cylinder heating controlled by programmer and cylinder stat?.
Yes - There is a cylinder stat - and the hot water Isn’t overly hot so it seems to be controlling it.

FAF1105B-ADB0-4C05-B921-A5F6FA61347C.jpeg



For reference, we have all tank fed showers and baths.
 
Last edited:
Water usage looks relatively static - although i cant go back any further than 2020

1642077430161.png




And this is an over view of Gas Usage

1642077629064.png



Also, something that may help. Octopus take half hourly readings on the smart meters. You can see here in the report i got that, when the heating turns off at 9pm, no gas is used over night until the heating turns on again at 6am. If there was a water leak, would i not expect to see usage over night as well? it also tells me that my tanks is relatively efficient at keeping the heat in.

1642077959500.png



on the 9th, it seems like the boiler did fire in the middle of the night

1642078153277.png
 
Last edited:
Somethings not adding up now anyway Steve. (maybe good)
You used 1257kwh of gas, apparently for HW heating. This equates to 43.4kwh/day for that 29day billing period. This equals to 36.9kwh/day at a boiler efficiency of 85%.
Assuming cold water at 12C heated to 60C, Litres of hot water = 36.9*860/(60-12), 661Litres.
This would equate to 1133 LPD at 40C.
Your actual water usage for both May and June was 460LPD for each month so ????.

Don't know how they came up with a estimated gas usage of 60550kwh/annum
 
Water usage looks relatively static - although i cant go back any further than 2020

View attachment 72749



And this is an over view of Gas Usage

View attachment 72751


Also, something that may help. Octopus take half hourly readings on the smart meters. You can see here in the report i got that, when the heating turns off at 9pm, no gas is used over night until the heating turns on again at 6am. If there was a water leak, would i not expect to see usage over night as well? it also tells me that my tanks is relatively efficient at keeping the heat in.

View attachment 72753


on the 9th, it seems like the boiler did fire in the middle of the night

View attachment 72755
You can see from the above that your "present" hourly usage is ~ 0.7M3/30min = 1.4M3/hour=15kwh/hr. or 13kwh/hr useful heat. Are you heating the whole house??.
Maybe turn the cylinder stat down from 60C to its very minimum and use the electric immersion say from 0900 to 1500 hrs tomorrow and monitor gas meter readings.
 
Water usage looks relatively static - although i cant go back any further than 2020
Er, it was ca 300 litres per day in Feb & Mar 2020 and then jumped up to >550 litres per day and has been slowly declining since then. When do you think that the increased gas consumption started?
 
Somethings not adding up now anyway Steve. (maybe good)
You used 1257kwh of gas, apparently for HW heating. This equates to 43.4kwh/day for that 29day billing period. This equals to 36.9kwh/day at a boiler efficiency of 85%.
Assuming cold water at 12C heated to 60C, Litres of hot water = 36.9*860/(60-12), 661Litres.
This would equate to 1133 LPD at 40C.
Your actual water usage for both May and June was 460LPD for each month so ????.

Don't know how they came up with a estimated gas usage of 60550kwh/annum

thanks for much for the detailed response john.g!

Ill try the Immersion Tomorrow and see if it makes a difference.

Does the immersion have a thermostat on it or will it just keep heating the water?

Er, it was ca 300 litres per day in Feb & Mar 2020 and then jumped up to >550 litres per day and has been slowly declining since then. When do you think that the increased gas consumption started?
is hard to pinpoint because the bills were 6 monthly back then, and now monthly.

Im trying to get hold of the orignal bills but Avro went bust - so i cant get them so easily!

Guys i really appreciate everyones input! thanks for taking the time to help!
 
Yes, The immersion will have its own thermostat, probably set to 60/65C. Make a note of the cylinder stat setting before turning down to minimum, it looks like (and should be) set to 60C.
 
Assuming cold water at 12C heated to 60C, Litres of hot water = 36.9*860/(60-12), 661Litres.
This would equate to 1133 LPD at 40C.
Your actual water usage for both May and June was 460LPD for each month so ????.
I wonder if the flow temperature being used to heat the DHW tank too low for the tank 'stat setting. E.g. if the flow temperature is 60°C and the tank stat is 65° then the boiler will cycle on and off all day keeping the heating loop that supplies the tank hot and, given there seems to be no insulation visible on the photo perhaps the losses from that would be enough to waste 2 kW.

Is there a programmer that limits the periods that the DWH tank is being heated for? It shouldn't need to be actively heated for more than an hour or two per day.

IME, the flow temperature needs to be a minimum of 5°C above the thermostat-determined setpoint.
 
I wonder if the flow temperature being used to heat the DHW tank too low for the tank 'stat setting. E.g. if the flow temperature is 60°C and the tank stat is 65° then the boiler will cycle on and off all day keeping the heating loop that supplies the tank hot and, given there seems to be no insulation visible on the photo perhaps the losses from that would be enough to waste 2 kW.

Is there a programmer that limits the periods that the DWH tank is being heated for? It shouldn't need to be actively heated for more than an hour or two per day.

Is there any way to confirm that?

The hot water is on permanently 24x7
 
Is there any way to confirm that?
Measure the DHW temperature from the closest tap with a 0-100°C thermometer. Check the flow temperature the boiler is delivering, which is shown on on its LCD display.

I don't like the way your cylinder stat appears to be away from the side of the cylinder. It should be secured in place with a strap. If the sensor is not in good contact with the pocket you'll have the boiler running continuously and will waste a lot of heat because the circulation loop will be hot 24/7.

The hot water is on permanently 24x7
Why? How much hot water do you use over the course of a day, and when. A programmer gives a good measure of protection from the above issues.
 
Measure the DHW temperature from the closest tap with a 0-100°C thermometer. Check the flow temperature the boiler is delivering, which is shown on on its LCD display.

I don't like the way your cylinder stat appears to be away from the side of the cylinder. It should be secured in place with a strap. If the sensor is not in good contact with the pocket you'll have the boiler running continuously and will waste a lot of heat because the circulation loop will be hot 24/7.


Why? How much hot water do you use over the course of a day, and when. A programmer gives a good measure of protection from the above issues.

Unvented so pocket stat with sensing bulb set to 50dc
 
i was told (rightly or wrongly) when it as fitted that they are so super efficient, that it can be left on all the time because they will only really heat when you use the hot water, because the thermal loss is so negligable.

However, your point is very valid that if there are issues, it could be heating all day!

The house would have 2 baths and 1 shower in an evening normally - so from a quick google, thats maybe 90L? tank is 210 - so if we just have the water on tomorrow for 2 hours at 12pm tomorrow, that should cover the day?
 
What is the cylinder stat set to now and what is the boiler temperature (set point) now, does this setting be changed in summer/winter?.

Two baths at 88 Litre/bath? and 45C is equivalent to 123 litrs of cyl HW at 60C so ~ 77 litres at 60C remaining = 128 litres at a showering temp of 40C = 10 min shower at 13LPM.
12kwh required to heat tank from cold so 2 hours should be fine as cylinder stat will cut out boiler anyway??.
 
Another couple of faults that need to be ruled out:

1. The CH zone valve were letting by when it should be closed. The CH radiator system would then act as a bypass for the DHW cylinder and waste a lot of heat in the process.

2. An incorrectly set automatic bypass valve (ABV) opening when the cylinder is heating.

P.S. Sorry if these ideas have already been discussed; I'm not able to read most of the posts at the moment because everything is covered in adverts.
 
What is the cylinder stat set to now and what is the boiler temperature (set point) now, does this setting be changed in summer/winter?.
Two baths at 88 Litre/bath? and 45C is equivalent to 123 litrs of cyl HW at 60C so ~ 77 litres at 60C remaining = 128 litres at a showering temp of 40C = 10 min shower at 13LPM.
12kwh required to heat tank from cold so 2 hours should be fine as cylinder stat will cut out boiler anyway??.
cylinder stat:
image.jpg

Boiler is on 6

image.jpg

We don’t generally touch them all year round.
 
Another couple of faults that need to be ruled out:

1. The CH zone valve were letting by when it should be closed. The CH radiator system would then act as a bypass for the DHW cylinder and waste a lot of heat in the process.

2. An incorrectly set automatic bypass valve (ABV) opening when the cylinder is heating.

P.S. Sorry if these ideas have already been discussed; I'm not able to read most of the posts at the moment because everything is covered in adverts.
1) any way to prove this option?
2) here is the external abv


A2A31730-8CF6-4ADA-B71D-C7C00557E8C9.jpeg

Is there an internal one in the boiler that may need checking.6B51A909-8E0D-4D68-962C-9A0FA4251F9B.jpeg
 
Turn the cylinder stat down boiler should go off if it’s heating the hot water
 
I’m pretty sure the house is calling for heat almost all day - and just no longer able to get up to temperature. Tado shows in the heat graphs as follows. The darker area shows when the boiler is firing constantly. The medium grey means it’s coming on and off a few times an hour apparently - and the light colour is off (this is heating only!)
The house is relatively well insulated, loft conversion to regs 5 years ago. Cavity wall insulation installed 10 years ago. Double glazed throughout.

When I discussed the issue with tado - they said looking at the graph for how the temperature drops from when the heating is off over night, the house only looses about 3 degrees over night - which he said was relatively good!

So could Chucks opinion that maybe something like a bypass not working properly - causing the water to go round and round instead of to the radiators be an issue?or something along those lines? Pump not pushing hard enough?
 

Attachments

  • F7DDC382-EA26-44F8-A27D-06370FD79DC8.png
    F7DDC382-EA26-44F8-A27D-06370FD79DC8.png
    258.1 KB · Views: 17
Can you see the actual boiler temperature from the boiler display to confirm that the high setting 0f 6+ is actually reflected in the boiler temperature.
Also, as suggested above, turn the cylinder stat up if the motorized valve is shut and ensure it opens and turn it down if the motorized valve is open and ensure it shuts.
If the boiler temperature is as high as it might be, 75C+, and if the DHW temperature doesn't feel scalding then a fair indication that its temperature is being controlled to its setpoint of 50C. (should really be 60C, for legionella protection).
 
Can you see the actual boiler temperature from the boiler display to confirm that the high setting 0f 6+ is actually reflected in the boiler temperature.
Also, as suggested above, turn the cylinder stat up if the motorized valve is shut and ensure it opens and turn it down if the motorized valve is open and ensure it shuts.
If the boiler temperature is as high as it might be, 75C+, and if the DHW temperature doesn't feel scalding then a fair indication that its temperature is being controlled to its setpoint of 50C. (should really be 60C, for legionella protection).
I tested the boiler stat - the valve was closed - I turned the boiler stat up and the valve opened. As soon as I turned it back down - the valve closed again.

Unfortunately the boiler doesn’t have a display - only the dial.
 
Ok then, the flow pipe from the boiler should be absolutely scalding and you should only be able to touch it for a very short time.
 

Reply to High gas usage for boiler. in the USA area at PlumbersForums.net

Similar plumbing topics

Had conventional boiler and tanks removed last year and new combi fitted and just recently had it serviced but the guy who did it has given me a...
Replies
9
Views
782
Hello Everyone. I'm back! It's been a year since my original post and I still haven't managed to resolve the mysterious water usage in my home...
Replies
37
Views
5K
MrsL6795
M
I have a Worcester Greenstar gas boiler circa 2017. There has been a noise coming from the boiler which resembles running water, I have checked...
Replies
2
Views
175
I have a Worcester Bosch Greenstar 15i condenser boiler which is about 13 years old. There is a separate hot water tank. Recently the fan in the...
Replies
3
Views
202
Hi everyone I currently work in oil and gas industry working in North Sea and further afield operating on high pressure oil and gas plants. This...
Replies
0
Views
887
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock