As suggested above make sure the system is properly dosed with inhibitor or you might be getting a hydrogen build up because of corrosion. Other than that the best way to prevent air ingress is to seal the system.
thanks

will add some inhibitor -

ref sealing the system -

do you mean - ensure the existing system has no tiny leaks anywhere?

or

do you mean - change the system design to one with some form of closed expansion tank ?

if the former - how do you go about tracking down any tiny leaks - there is certainly nothing obvious visible - so is there a recognised method for doing this ?
 
The later...removing small feed and expansion tank in loft and replacing with an expansion vessel and a filling loop.

You can't really trace a leak without visually locating it unless you put some cheap strong cologne in the system and have a sniff around (never done this yet btw) or have the system pressure tested. If you suspect a slow leaking pipe or valve it's common to wrap a bit of tissue paper around the area to see if it becomes damp over time.

One advantage of sealing the system is you can tell straight away if there is a drop or change.
 
OK thanks for the input

latest

bled the system yesterday - lots of air in the upstairs radiators - all of them - not just a bit - my guess is several litres in each

central heating ran fine - and all radiators got nice and hot all over ( after bleeding) - no gurgling noise after it started up /first 30 seconds

started the HW today and again loads of air in the system and boiler is now throwing an error code - FD - which according to Ideal Logic is _ no water detected in the boiler - which makes sense given the huge amount of air in the system.

so - narrowing it down
- it cannot be hydrogen build up producing this much volume of gas overnight - so it has to be from another source

- there are no places in the house where even 1-2 litres of water could leak out of a pipe and not be visible - most pipes are exposed and visible and show no leaks - there are just a few short runs under the floorboards upstairs - and none under the ground floor floor and i think if a few litres of water were leaking into the space under the floorboards it would start to be visible through the ceiling - i am assuming for many litres of air to get in, the same approx. amount of water has to come out / go somewhere

so does this mean the air is for some reason being drawn in through the expansion pipe / overflow

if so what would cause that ?
 
Yes, sounds like air is being drawn in by the vent pipe, do the suction test as mentioned earlier by our friend Tamz.

Could be poor positioning of the F/E pipes in relation to each other the pump, or if pump has been changed neutral point has changed. Turning down pump speed may help.
 
Yes, sounds like air is being drawn in by the vent pipe, do the suction test as mentioned earlier by our friend Tamz.

Could be poor positioning of the F/E pipes in relation to each other the pump, or if pump has been changed neutral point has changed. Turning down pump speed may help.
cheers - i will take a look

interesting that it doesn't do it when n Central heating - only on HW

will take a photo of the pump/pipe layout and post it in case it sheds any light
 
Last edited:
here is the pipework around the pump and the motorised valve.
its hard to get in there to get a decent photo that captures everything clearly without one pipe obscuring another - but i have


labelled
boiler pipework.JPG
where they go in the hope that it helps
 
No, if I understand it correctly the F/E pipes are positioned as such that it can't but help suck air into the system, usually they're positioned differently and behind the circulator (pump) . There should be a pipe feeding the pump from beneath, where's that coming from because that should be coming from the boiler and the pipe you've labelled "To boiler " going to radiators.

boiler pipework.JPG
 
hey, thanks for your input !👍

i have just checked the pump direction and i do believe its direction of flow is in the direction you indicate. i couldn't find any arrows on it - and there is nothing in the user manual - but the shape of the casting shows the fitting at the bottom goes to the centre of the impeller scroll - so its sucking from the bottom and pumping upwards

in terms of air getting "sucked in" through the expansion pipe - what i don't get is that the water feed and expansion take off both appear to be on the "high pressure side" of the system.
by high pressure i just mean that the coil in the hot water tank are downstream of the expansion pipe - so to my novice brain - i would have expected the circuit to be boiler - pump - expansion pipe take off point - coil in hot water tank - back to boiler

so assuming there is some restriction due to friction in the coil in the hot water tank - on starting the pump i would have expected positive pressure at the point where the expansion pipe is taken off - so i would have expected it to try to push some water up - at least a little against gravity - rather than draw air in -

what am i missing / do i have it wrong ?

will add a couple more photos in case it helps

mot valv and bypass.JPG
pump lower.JPG
 
Have a google of any open vented diagram, the F/E pipes are always behind the circulator on the circuit and never in front, that is the cause of your air ingress issues.
 

Reply to Help! - Noisy central heating system – not heating water well …… in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Hi All, Hope somebody can help :) I have a vented HW system with a pressurised Ch system but got bit of a annoying issue, when the hot water...
Replies
3
Views
492
Hi, We moved into a new property yesterday and are a little baffled by the heating/water tank situation. The previous owners unhelpfully left any...
Replies
3
Views
358
I have been facing central heating low pressure on unvented hot water RM Cylinders but can't see any leak on the PRV, expansion vessels and...
Replies
2
Views
502
losing pressure
L
  • Question
Have a sytem boiler with unvented cylinder with 2 heating zones plus hot water in a house we moved into recently. To start with we were always...
Replies
8
Views
445
Hi, Over the past few months, my wife and I have noticed a constant pulsing sound throughout the house which is particularly noisy at night (this...
Replies
4
Views
677

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock