3
Hi, I'm new to this forum so I hope I've posted this in the right place. I installed a Grundfos UPS2 15-50/60 (part number 98334549) circulating pump into my oil fired central heating system 4 years ago. Recently on the boiler firing up the pump has not started, there is an intermittent ticking sound as though the pump is trying to start but can't. After about 10 to 15 minutes the pump will start and continues to run until the system turns off. This is currently not causing me any issues, other than worrying that there is something waiting to happen. My thoughts are that it may be the run capacitor not having enough umph to start the motor turning but I'm not sure why the temperature of the pump (as this seems to be a factor) results in the pump then running. Having looked into the top of the control box on top of the pump I cannot readily see the capacitor (on the Grundfos pump I replaced the capacitor was readily visible and easily removed/replaced) and I was wondering if anyone on this forum had any advice on how to replace the run capacitor in this particular model. Any help or advice would be greatly appreciated.
 
I think these type of (smart) pump motors may not have a capacitor as they are actually a brushless DC motor.
If you isolate the pump electrically and shut the two isolation valves you should be able to then carefully remove the pump head & impeller and it may then only require a good clean up.
 
sounds like the capacitor is weak / dead
 
Does sound like a capacitor fault. They can be tested a couple of ways, either with a multimeter set to test capacitance or any multimeter set to read resistance. Any doubts about locating the cap then contact Grunfos, although its got to be there in the control assembly.
 
Thanks for all the replies. Water is clean enough so I don't think it is that, as I said I think the problem is the capacitor but don't know how to get to it in this particular pump. Tried contacting Grundfos but they were no help. Anyone out there with any suggestions as to how to locate it (if it exists!!!), need to find it before I can test it!
 
 
There was an issue on a pump manufactured around that time. A few I came across had a component that didn't like energy spikes. If you are at the end of the 'grid' or have old equipment which could interfere with the supply to the pump, it may be that. Can't say for certain but it sounds like it.
 
I think that pump is a DC Permanent Magnet so does not have / need a capacitor to start. Having said that, if you have removed the cover and cannot see a capacitor - go no further. If it has a capacitor it will be easily accessible.
 

Reply to Grundfos UPS2 15-50/60 circulating pump problem in the Oil and Solid Fuel Forum area at PlumbersForums.net

Similar plumbing topics

Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
293
PSxxxxxx
P
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
465
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m...
Replies
6
Views
326
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason...
Replies
3
Views
343
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is...
Replies
5
Views
562
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock