Burnt my head out this one!

Internal filling loop, Soding out when try to fill.

Fitted new one, couldn't get pressure above 0 bar f9 starts flashing.

Checked on low water pressure sensor with multi, was saying that I've got 2.5 bar of pressure in system when check white and orange wires I think it was to earth.

Drained system an took sensor out that had crap in it and refilled.

Same, f9 and 0 bar.

Now I'm not sure whether by me linking the over heat stat or pushing the manual pin in, the pressure went up then to 0.4 bar, getting somewhere.

Next thing I've got no bloody display on the boiler !! I'd switched off at fuse spur and thought it had took the board out.

Eventually got it back on after speaking with glow worm, not sure how we got it on but it come back on eventually.

Now when I try to fire boiler, it gets to ignition but literally cuts dead on the 3rd ignition attemp and goes to f9 again, doesn't attempt at any stage to light again.

I'm just seeing if anyone has had any issues similar with low water pressure sensors ?

If it's the board it's not worth me getting involved, it's cheaper for glow to fix.

Thanks
 
I’d go with the sensor mate it senses the system pressure an also looks for slight rise in pressure when the pump kicks in (think around 0.2-0.3 of bar) never had much luck trying to clean them out.
 
I’d go with the sensor mate it senses the system pressure an also looks for slight rise in pressure when the pump kicks in (think around 0.2-0.3 of bar) never had much luck trying to clean them out.

With me linking the ohstat out, I managed to get pressure to over 1 bar but boiler wouldnt fire.

The thing that's got me concerned with board is, it went off and couldn't get back on again ? Glow worm had me disconnecting bits on board and they had me checking DC voltage at j13. I was getting like 5 - 7 DC it should of been 13 - 16 dc.
 
Sorry just re read properly where you said you linked OH stat out,f9 can relate to overheat or water pressure sensor failure I think depending if it’s an older style pcb. Just looked at MI’s yeh the J13 is the checking between the main pcb an user interface,I take back my previous comment does look more likely to be pcb :(
 
Sorry just re read properly where you said you linked OH stat out,f9 can relate to overheat or water pressure sensor failure I think depending if it’s an older style pcb. Just looked at MI’s yeh the J13 is the checking between the main pcb an user interface,I take back my previous comment does look more likely to be pcb :(

Ive spent that much time messing with it today that I want to sort it.

The PCB is putting me off though!

I've left it with the landlord, basically said if I fit new pressure sensor, oh stat and forgot to mention prv and everything stats working then using me works out better, glow worm would cost her.

If I have to fit a board it's cheaper using glow worm, let her decide.
 
i would suspect the main or user interface board fault , i would also check the sequence with the low voltage plugs disconnected one at a time also handy when you have no display as normally its the low voltage components that causes that . you should also be doing continuity checks on the harness connected to th pressure sensor and other low voltage side as well
 
i would suspect the main or user interface board fault , i would also check the sequence with the low voltage plugs disconnected one at a time also handy when you have no display as normally its the low voltage components that causes that . you should also be doing continuity checks on the harness connected to th pressure sensor and other low voltage side as well


Cheers

Im going to spend an hour on it before ordering PCB.
 
Status
Not open for further replies.

Reply to Glow worm 30ci F9 fault in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
139
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
206
P
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
140
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
339
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
252
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock