Just in the process of planning a kitchen, but I am confused about the clearances required for a gas hob. Electric is going in now, but might as well make sure that space is left to allow a gas hob.


If wall cabinets are fitted adjacent to this the hob area is an additional 50mm each size required? Is the cabinets are above 400mm from the worktop, is this clearance still required.
 

here you go
this shows that if the wall units are in line with the edge of the hob they need to be at least 460mm above the hob, any lower than 460 mm from the hob requires them to be set back 50mm either side from the vertical
 
Last edited by a moderator:

here you go
this shows that if the wall units are in line with the edge of the hob they need to be at least 460mm above the hob, any lower than 460 mm from the hob requires them to be set back 50mm either side from the vertical


my pic was here last night, if you need the pic(its from the BS then send me a PM with an email address and i will send it on)
 
cooker clearances.JPG

You need a talk with yer boy Kirk
 
Status
Not open for further replies.

Reply to gas cooker clearances, cabinets above 400mm from worktop in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, I'm wondering if anyone can help with a query. We have recently had a new kitchen installed and are arranging for our freestanding gas cooker...
Replies
2
Views
1K
Just to be really clear I will not be doing any of the work mentioned below. This will all be carried out by Gas Safe Engineers. We're in the...
Replies
4
Views
3K
Hi, sorry this is so long. I have tried to give all relevant info. We are building a new, small, two-storey house that is off grid for power...
Replies
3
Views
933
Hi. I have been on the phone to the Gas Safe Register, who have pointed me a bit in the right direction looking for certain information. I am in a...
Replies
3
Views
3K
Hi all, I have a Heatmiser UFH installation, 7-8 years old now. This week we noticed that a few of our heating zones were not warming up, even...
Replies
1
Views
1K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock