I am receiving conflicting advice on whether the fill and expansion pipes on our new system are the wrong way around and the cause of air noise at the pump weeks after installation as well as the magnaclean keep gaining air.

We frequently get air bubbling noise in the pump even after repeated bleeding of rads and other vents including the magnaclean fitted downstairs above boiler (system has 18 rads).

This is the current arrangement so any thoughts on whether the fill/expansion are the wrong way around on the 'H' arrangement and whether that could allow air to be drawn in:

Pump pipes.jpg
 
Edit ..... brain fart , earlier reply wrong . sorry yes its wrong vent first , then fill , then pump , ideally on horizontal pipe work and closer together if poss and ditch the two elbows if poss
 
Last edited:
Can we see a more distanced photo? Also how far away is the tank from the pump (very long shot that its pulling air through)
 
Ideally it would be on horizontal pipe work and all closer together .
 
Thanks for the info so far and sorry for the delay in replying - notifications end up in the spam folder.

A wider view is:
Pipework.jpg

The height from the pump body to the bottom of the expansion tank is 2.35m (and almost directly above in the loft). The top of the expansion pipe loop is 0.4m above the tank water level.

Even to me the fact that the pump is pulling on the vent instead of feed seems odd but I wasn't sure if that would be enough to cause the air issue.
 
Status
Not open for further replies.

Reply to Fill and expansion wrong way around causing air ingress? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

When I turn on our CH there's a lot of noise from one specific part of the system - the pipes on the landing, and one radiator. It sounds like...
Replies
35
Views
1K
Hi, I have had this problem for a week now. The oil boiler will run for a short while and then stop. If I check the pipes around the 3 way valve...
Replies
3
Views
836
Hoping somebody can help, So, in a nutshell… Standard 90s Westbury home – condensing boiler, pump, wall thermostat, etc etc... Normal, common or...
Replies
8
Views
567
Hi there, I recently replaced a dead central heating pump in my home, so drained down the system completely, fitted new pump and filled up. What...
Replies
1
Views
714
Hi there, I recently replaced a dead central heating pump in my home, so drained down the system completely, fitted new pump and filled up. What...
Replies
11
Views
1K
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock