Got issues with a fan on a boiler and wondered if there was anyway of telling what the negative and positive pressures should be?
 
It just need to be enough to activate the pressure switch.

Check the data on the APS
 
Can only see a maximum pressure on it. Not sure if there's enough negative but the fan seems to be doing fine.
 
The pressure on the APS is that point it activates no min or max. Just use a gauge on the venturis or tubes to see the pressure your fan is producing.

What issues are you having?
 
Boiler goes into fault about 5 seconds after lighting.
Works ok with case off or negative hose disconnected from APS.
Replaced hoses as they'd gone brittle with heat.
Removed fan, cleaned venturi but was fine.
Swapped APS and same problem.
Flue looks ok and fan spins well.

Think I might be having a "moment" with this and it's something glaringly obvious
 
If the blades are dirty the fan spins but it wont shift any air, the pressure test will show this up though.
 
Cleaned the blades with a brush and air duster when I took it out to check the venturi that sadly wasn't blocked :-(
 
Have you tried taking out the restrictor ring if it's fitted?

If it works with the case off then the fan can shift enough air, putting the cover on restricts it down. You'll probably find its the fan but I'd take the ring out first.
 
Status
Not open for further replies.

Reply to Fan Pressures in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, I have a Worcester 28i junior boiler that has started to lose pressure, only when using the central heating. When using hot water I have no issue, however, when running the heating the pressure drops. Im looking for some ideas on what could be causing this. I have no sign of pipe leaks...
Replies
6
Views
227
P
  • Question
Boiler is SIRIUS THREE FS 70 Potterton commercial. Situation: We are small building contractors and my labourers managed to damage the radiator pipes during the strip out. Not the end of the world as damages happens. I am responsible builder and paying my bills and to repair the damages if...
Replies
2
Views
87
I have done pressure test for 2" high pressure pipe line by closing the pipe with rubber plugs at the ends. It was 3 bar and I kept it for 24 hours. Its shows a pressure drop of 0.5 bar. The pipe line is fully exposed and I couldn't find any leak on them. What might be the problem. If somebody...
Replies
6
Views
240
Hi, I'm looking for a water pump to pump water from a storage tank at a constant 3 bar pressure. It's at a campsite I run that's at the bottom of a long, steep hill. We struggle with very high and often fluctuating (around 7 bar) water pressure, which wreaks havoc with our water heaters. I've...
Replies
2
Views
79
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
523
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock