bewsh

Plumbers Arms member
Plumber
Gas Engineer
Messages
612
Baxi Bermuda, gravity h/w, pumped c/h.

Whenever customer turns the boiler off on the clock the electrics trip. So I thought must be faulty switch on programmer, so fitted new programmer and tested but the same problem.

Investigated further and found 106vac on the earth connection to the room stat, no voltage on any of the earths at the programmer, and different colour wires coming in to the stat than what leave the programmer, so guessing there's a fault with a wire somewhere which a earth is touching a live or something.

But I would have thought that the voltage on the earth should trip the electrics anyway?

And sometimes when you turn the boiler off at the programmer, it only trips a certain circuit on the consumer unit (not sure which circuit as nothing labeled), but the heating circuit is still live?

Anyone got any ideas?
 
If it were me and there was nothing obvious, I'd strip out cables and start again checking all electrical components as you go
Has it got a 2 port and stat, or just power from clock straight to pump/boiler
 
turn boiler off at fused spur and test earths if theres still voltage you need a spark

if theres no voltage need to test each component until you find it
 
The earth wire on the stat may not be connected to earth, so it could be feedback from other cables, you need to find where all the cables connect and check them out.
 
No power if fuse spur is off.

The room stat doesn't actually work either, if I take it off the wall and just leave the wiring in place, the boiler still fires up.

I think the problem is with the wiring to the stat, I think I'll try disconnect that wiring and just fit a wireless stat next to the programmer.

And no, there isn't a 2 port, just a feed straight to the boiler/pump (supposed to be through a room stat)
 
No power if fuse spur is off.

The room stat doesn't actually work either, if I take it off the wall and just leave the wiring in place, the boiler still fires up.

I think the problem is with the wiring to the stat, I think I'll try disconnect that wiring and just fit a wireless stat next to the programmer.

And no, there isn't a 2 port, just a feed straight to the boiler/pump (supposed to be through a room stat)

i would say prob room stat but not unheard of boiler going to earth
 
Status
Not open for further replies.

Reply to Electrics tripping when turning boiler off in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

We've had a Grant Thornton oil boiler for about 5 years and suddenly it trips the electricity when it rains? The unit is in a wood shed and the...
Replies
2
Views
418
I have a Worcester Bosch Greenstar 15i condenser boiler which is about 13 years old. There is a separate hot water tank. Recently the fan in the...
Replies
3
Views
202
Good afternoon, I am experiencing a pressure issue with my heating system and was hoping to receive additional insight as to what the problem...
Replies
9
Views
403
Hello, I have quite low flow rate for my electric shower (a piddling 5L/min), and would like some tips or advice about how to solve or find the...
Replies
14
Views
894
Essaboy
E
Hi I have a fully pumped heating system fitted with a Drayton MA1 diverter, after the summer run the heating stopped coming on, so I replaced the...
Replies
3
Views
617
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock