As stated, by doing it right such that courts aren't involved. Time to shut this down guys. Night Night:8:
 
All showers must be fitted with 10mm twin and earth minimum, terminating at the consumer box with a separate RCD for safety.

Sorry, not all at all. Power showers only need a 3A fuse and 30mA RCD. 2.5mm cable will be fine.
 
Last edited:
To take the load without overheating the cable. All showers of 8.5kw and above must be 10mm twin and earth minimum. If the cable run is a long one it should be increased to 12mm.

You have got that one wrong.
It needs to be suitably sized to suit the load and how it is run.
A bit like saying a 24kw boiler needs an 22mm gas pipe. It doesn't necessarily but it does need a properly sized one.
 
You have got that one wrong.
It needs to be suitably sized to suit the load and how it is run.
A bit like saying a 24kw boiler needs an 22mm gas pipe. It doesn't necessarily but it does need a properly sized one.
Yes that is what I said, it should be sized to suit the load and run, and increased if the run is a long one. But 10mm is now the minimum and any M.I I've read recently states this.
 
New posts
Status
Not open for further replies.

Reply to electric shower problems in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, I have fitted an electric shower, teed off the toilet cold feed (Mains) The pressure for the shower is very very poor just dribbling out...
Replies
9
Views
318
    • Like
Hoping someone can please help. I have an intermittent fault with my electric hot water. I have an older style electric hot water service that...
Replies
6
Views
467
Hello, and thanks for taking the time to read. I'm trying to work out if the idea I have is practical? The water pressure in my newly renovated...
Replies
3
Views
417
S
  • Question
Been getting large amounts of sediment coming through the electric shower. Had two plumbers look at the job who are unsure of how the sediment...
Replies
3
Views
509
Hi and thanks for the welcome to the forum. I am a DIYer and need to take off and reinstall my Aqualisa Aquastream to remove the tiles before...
Replies
5
Views
400

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock