Yes correct, but doesn’t prove it works properly, hence the additional testing and don’t forget the link.Thanks so testing neutral to live in. With a reading of 240vac between the ports. Shows I am getting 240vac to the stat.
YesDoes testing neutral to switch live on demand with a reading of 240ac show that switch live is sending power to the boiler. Making a circuit when there is a call for heat?
Thanks yes I will make sure it's wired in to the boiler.Yes correct, but doesn’t prove it works properly, hence the additional testing and don’t forget the link.
No:Thanks just trying to find the wiring diagram. I think Live is 1. Neutral 3. Switch live 2. ?
Thanks what Shaun said to test makes more sense now!No:
1 should be live in
3 should be switched
2 should be Neutral
Wiring diagram usually on the reverse of stat cover.
To to check I'm on the right track. Testing 3 (switched) to earth or neutral with the stat off. A reading of 0v. Shows that no volts are passing though the circuit i.e no call for heat at the boiler?Test terminal 3 to earth or neutral with stat off should be no voltage
If there is 240v check 1 if that’s got 240v aswell stats dead
Yep, me too. Had one recently, set to a mid point, so in winter it’s fine. The way it was wired max was off and low (5 degrees) on the VRT30 was off.Correct but I have seen them wired backwards eg 3 live 1 switch
Thank you!Correct but I have seen them wired backwards eg 3 live 1 switch
Thanks of wired backwards at the stat it would still work? I know if get the wires wrong when swapping a boiler at the boiler side the stat comes on when turned down and off when turned up.Correct but I have seen them wired backwards eg 3 live 1 switch
If that stat was dead, would that cause it not to knock off the heating. As is happening. ThanksTest terminal 3 to earth or neutral with stat off should be no voltage
If there is 240v check 1 if that’s got 240v aswell stats dead