Discuss Combi boiler stat not turning off heating in the USA Plumbers Advice area at PlumbersForums.net

Matt0029

Gas Engineer
Messages
1,143
If the stat is not shutting off a combi boiler (analogue stat Honeywell) even though the stat is clicking when turned up above the room temperature. What are the likely causes. Unless it's never been wired right from the start up. Thanks.
 
I just wondered if the stat can still be the fault if it is clicking when turned above and below room temperature? This is the stat?
 

Attachments

  • Screenshot_2021-08-11-19-33-03-949_com.amazon.mShop.android.shopping.jpg
    Screenshot_2021-08-11-19-33-03-949_com.amazon.mShop.android.shopping.jpg
    197.9 KB · Views: 7
Just going to download the instructions. But to test would I be looking to see if I get 240v between live and switch live?
No mate, testing that you’ll probably get 120vac.

Test Neutral to live in (should be terminal 1) - 240vac
Test Neutral to Switch live - on demand - 240vac
Test Neutral to switch live - on satisfied (or stat at lowest) - should be 0 Vac
 

Reply to Combi boiler stat not turning off heating in the USA Plumbers Advice area at PlumbersForums.net