He pump has gone and needs replacing. It has a celsia tf110 230v-50hz. What grundfos would be replace this please. Ive seen grundfos ups 15-60 pump 96281473.

Thanks
 
In the real world Mrs Noheat wants it fixed.
She rings you for a price. You say sure a new A rated pump that will save you 20p a week on your leccie, supplied and fitted for £200
She rings the next guy who says no probs i'll fit you a pump (any pump, myson, screwfix shyte) for £150.
She takes the £150 offer and he got the job and made about £50 more than you would have at your £200 asking price. Her heating is working and she couldn't care less about 20p a week and if it breaks down again 2 years later such is life.
That is the reality i'm afraid, no matter what some bureaucrat says must be done to save the planet if indeed it really needs saving.
Devils advocate :smile:

So offer your customer 3 options:

A rated expensive branded pump @ £high price
A rated less expensive unbranded pump @ £mid price
Non A rated cheap pump @ £budget price

I bet most of them take the middle option.

We find that all the time - if we offer 2 products which do much the same job, the cheapest one sells most.

If we offer 3 products that do the same job, the middle-priced one will out-sell the other 2 put together.
 
You will probably find most Alphas will be set to CP2 just to be sure it works
To cast that in numbers:
System x conventional pump 4.5kW/day
Alpha 2L CP2 1.5kW/day
Alpha 2L III 3kW/day

VPs can not get used in the system as causing lock out by overheating since the ABV does not open (fixed setting).

Now do the maths with your 20p/week.
 
To cast that in numbers:
System x conventional pump 4.5kW/day
Alpha 2L CP2 1.5kW/day
Alpha 2L III 3kW/day

VPs can not get used in the system as causing lock out by overheating since the ABV does not open (fixed setting).

Now do the maths with your 20p/week.

There must be a lot of hours in your day :wink:
A 15/50 draws between 40 and 90 watts /hr depending on how it is set. Speed 1 running 10 hrs a day 400w or speed 3, 900w. electric @15p/kwh is 6p/day(10hrs) on speed 1 or 13.5p on speed 3.

An Alpha draws between 5 and 30 odd watts depending on how it is set or is working so say on average for easy counting it is drawing 20w.

You are saving 3p/day (21p/wk so i wasn't far out at 20p) compared to a 15/50 set on speed 1 or 10.5p against one set at speed 3. Even if it constantly drew 10w (which it won't) the saving would only be 4.5p/day

4.5 years (or 1.5) to get your money back on the extra 50 quid the pump cost.
As you say they can't be fitted alongside an abv so add in the cost of stripping that out or fitting a thermostatic controlled one and your customer will be dead before they recovered their costs.
 
The central heating system is shared and has it's own meter (single slot meter).
The reading includes boiler and controls. Continuous OTR is meant to set the flow temperature.

And it surely is not a 15/50.

Yes the pump does do long hours. In this case the saving is 3kW/day at 15p. The saving per month in this case (admittedly extreme) is somewhere around £13/month.
 