Am unable to find a clear answer to this -

But the water in the cistern with BS 1212 part 2 float valve what is the highest water category that it can be?

Im thinking category 3 has in F and E tank not been able to find anything written in WRAS guidebook.

Can anyone clarify this?
Thanks!
 
Cat 5 if you drill the holes to spec
 
Hi thanks so far but just normal tank with 1212 part 2 valve With out adding extra weir holes into it.

Correct only thing overflow must be sized correctly and terminate to outside

If into stack / waste pipe needs to have an air gap

Weir holes is an AA air gap

IMG_3651.PNG
 
What you planning on doing that's cat 5 risk ?
 
The rainwater harvesting set ups are generally cat 5 due to potential for bacteria etc so yes you would be correct to assume the pigeon faeces would be a cat 5 risk, therefore a suitable back flow prevention set up would be required to provide the appropriate backflow protection against the risk described suirable AB. AA air gaps etc pipe id
 
The use of a BS1212 part 2 float valve does in its self guarantee the air gap it just helps with the amount of water that can be stored & still maintain the air gap.
It always down to the Plumber to drill the holes in the right places to achieve this, air gaps are dependant on the size of the inlet & overflow.
 
Correct only thing overflow must be sized correctly and terminate to outside

If into stack / waste pipe needs to have an air gap

Weir holes is an AA air gap

View attachment 33924
Sorry Shaun but a weir overflow is an AB.
AA is where inlet is above the cistern overspill & free falls into the cistern. Both however are good for Cat 5 & are the only ones that should be used for a rainwater storage if that is what the OP is doing.
ref - WRAS book 6.13
 

Reply to BS 1212 Part 2 Air gap in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi all, Got a nightmare situation with a central heating system I recently adopted. It's an open vent system with a combined F&E pipe, with a...
Replies
17
Views
2K
Hi, I've got a leak coming from the loft into a bedroom which I think is caused by water overflow from feed and expansion cistern (see attached...
Replies
13
Views
2K
    • Like
Hi all, We recently purchased a house and nothing seems to work correctly here, I've spent weeks rectifying issues. Plumbing, electrical...
Replies
47
Views
5K
So I bought my first flat recently (am in UK) and in a bit of a pickle as the bathroom has turned up lots of problems that weren't picked up by...
Replies
1
Views
730
Hi Guys, Been having a real saga and head scratching situation. I originally had 1 problem, and now 2. Original issue: Air being built up in...
Replies
17
Views
4K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock