I have an Ultracom 30HXI that serves DHW, Radiators and UFH manifolds. The boiler is experiencing short cycling problems and I have had a heating engineer attend twice now and he is unable to diagnose. The problem is as follows: When there is call for heat the boiler fires and heats the water, but only heats the water until there is a 14 degree flow/return difference - I have checked the values via the boiler diagnostic menu. It then cuts out, the flow temp drops and then within seconds it fires up. Heats the water again until a 14 flow/return difference. It continues in this cycle of fire, cutout fire etc until it reaches the flow temp set (in this case 70 degrees) so long as the return is not greater than 14 degrees difference. The boiler will then modulate its power and continue running; however once more than 14 degrees it cuts and continues its cycle again and again. The upshot is that it takes ages to fully heat the house. Are you able to advise on likely problem (or is this as design) such that I can direct my heating engineer to replace the correct part. The condensate trap has been replaced (as it was leaking) and the boiler has recently in the last six months had a new fan / service.
I have also posed the above to Glowworm technical support
Andrew
What happens if you just turn the rads or hot water on ?
Thanks for the reply.
If I start from cold and just put the radiators on it does exactly the same. Heats till 14 degree difference, shuts off and then back on again in a few seconds. Repeating until it reaches set flow temp so long as difference no more than 14 degrees.
I went into boiler diagnosis mode where it would display the actual flow and return temps it is receiving.
If I leave just rads on and let it keep doing its cycles until it gets to max temp it modulates fine. If I then switch on the UFH and introduce some more cold into the return it goes back to its cycles. Eventually return increases and it will again modulate at the 70 degree set flow temp so long as difference does not go more than 14 degrees.
Thanks Andrew
That defo doesn’t sound normally have you measured the temp on the pipes also how old is the pump ?
Pump is new as thought I that was the problem. It is better with the new pump - I think my previous was slightly undersized.
Yes have measured temps on the flow and return and whilst the reading is not the same as the boiler showing they are within about 5 degrees. My heating engineer was going to replace both the flow and return thermistors, but I am reluctant given they are £30 each plus his labour - albeit an easy thing to replace.
Yea within 5 is fine have you tried lowering the flow temp to 65 ?
What speed is the pump on ?
Presume you got the boiler return temp from d.41? through Diagnostic menu Level 1 so you should be able to access the S parameters by selecting d.99, this should give all the S parameters?
Ah yes D99 - It is showing S04 and then when it cuts goes straight to S03 and then S04
I did try reducing pump speed again today to PPA curve. It is still cutting out, but stays on longer and lets the flow/return differential go much higher, circa 25 degrees
So only 2 of S codes, S.03 & S.04 which are ignition on and burner on, a bit strange that no other S code up when the burner stops, normally if the burner cuts out on say the boiler flowtemp exceeding its SP by 5C (where the boiler min output is greater than the heating demand) then you will get a S.08, the anticycle time.
You might look for a F (fault) code when next it stops, one would think though that if a fault code is flagged that you would have to reset the boiler?.
Not sure if available at your boiler output but you might try setting d.0, Heating Part Load, to say 10 or 12kw and see if any difference.
Where do you get these settings? "pump speed again today to PPA curve"
Thanks, No F codes and just S03 and S04.
Will try the d0 setting, it is set to max at present
My pump is a Lowara Ecocirc L-plus 25-8/130 which has 3 fixed speeds, 3 constant pressure curves, 3 proportional pressure curves and an auto adapt curve
Why such a big pump how many rads ?
Does that pump display the head(M), flowrate(m3/hr) and power(W)?, if and if d.0 is settable then if the max output is set lower than the heating demand then we can calculate the dTs etc from this and compare them with the boiler readings.
Thanks for the continued responses.
Yes the pump does display all of that and yes according to the manual d0 is a writable value - Given this is a large house though what should I set to?
Boiler is a 30kw boiler.
I have 8 radiators which are each circa 4000 BTUs each at delta T 20.
I have 2 underfloor manifolds - each manifolds supports 7 pipe runs that are each circa 80 metres.
One manifold is fed with 28mm pipes as it is a long run
The other manifold is fed with 22mm pipes
The UFH is set at 45 - 50 degrees on the mixers
Plus DWH with a 250 litre tank.
Just now, if (when) running continuously, note those pump values and also d.40 & d.41 and we can compare them.
Preferably with rads only on.
Are the ufh manifolds got there own pump set ?
Boiler is modulating fine at present.
Just rads calling for heat (and maybe DHW), but UFH off
Flow is 70 degrees, return is 49
Pump is reading - 8.2 Watts, 1.2 metres head and 0.8 m3/hr
I checked d0 and it is set to 30
Andrew
Thats a amazingly low head, anyway, by calculation, using the pump flow of 0.8m3/hr and the boiler dT of 21C gives a boiler output of 19.53kw, the 8 rads at rated output = 9.4kw but because of the flow/return temps will be outputing ~ 74% of their rated output, say 7kw. So 12.53kw going elsewhere??.
If the pump values are still similar suggest reducing d.0 to 15kw, if the above boiler output is valid then the flow/return temps should reflect a 15kw boiler output and would confirm that d.40 & d.41 are reading accurately.
Does your system have a low loss header or close coupled Tees as the very low head seems to indicate this and the pump is on the lowest PP setting A, I can't see any PP or CP settings, apart from A,B or C for this pump (for interest), do you have any values/ranges for them?.
Dont believe there is a low loss header and no close coupled tees. Just a standard bypass valve
Re the pump again not really sure which setting it should be on, assume PP as I have rads with thermostatic valves, but pump also has the eAdapt setting, constant pressure and also fixed speeds
If I run the pump on curve B or C then the head and flow increases.
I found this for the specs on the pump
The pump curves are in your attachment, I reckon that you would get ~ 1.1m3/hr @ 2.1m on PP B and ~ 1.4m3/hr @ 3.6M on PP C.
This doesn't solve your problem however, theoretically PP C should reduce the dT from 14C to 8C and allow the boiler to get closer to its SP temperature before recycling and might reduce the 20C dT to 11.5C even though no problems with the boiler once it reaches its SP.
Have you reduced d.0??.
Interesting,
I dropped D0 to 15 and set the pump to PPB and it stopped cutting out. But it did not appear enough to heat the water. I had rads on and one UFH circuit at the time.
Then all circuits started calling for heat so increased d0 to 25, It started its cutting out. Gradually reduced D0 to 21 where it appears not to cut out, this is with most of the circuits on, but it is taking much longer to heat up, although not cycling.
Pump is showing circa 3.5 metres head and 1.5 m3 flow this is on curve B
Should I be using curve C?
Not having any heat loss calculations for my house again dfifficult to know what boiler should be on.
This is really interesting stuff, my plumber / heat engineer never discussed any of this.
Easy enough to do go round and calculate the size of your rads and find similar ones on the internet there output will be listed so Calc all the rads and total it up
Then give us the flow rate of each ufh loop via the flow meter and we can work out the rough load ufh wise
Interesting,
Does the cycling still only occur when the dT reaches 14C?.
You can calculate the boiler output at any given time by
(m3/hr16.67x60xdT/860)kw, At 14C dT, boiler output is (1.5x16.67x60x14/860), 24.4kw. So if rads only on easy to calculate their combined output once you also note the boiler flow/return temperatures.
A flowrate of 1.5m3/hr, 1500LPH should result in a Hx dP of 3.6m, 2.38x(1500/1220)^2, but your pump is only developing 3.5m so something not adding up?, boiler internal or external bypass passing, or another pump hidden away some where?.
Even If the boiler has a internal bypass thats faulty presume the boiler will still measure the flow/return temps correctly.
The pump, judging by your original pump values for PP A seems correct, can you just post the power W + flow & head while running in PP B and we can soon tell if these values add up.
So boiler settled down and is modulating ok now
flow = 70, return = 58
Pump is running at 26 Watts, 3.7 metres head and 1.42 litres per second
I have rads on, DHW is on, but not sure if calling for heat
Two UFH zones are on (on seperate manifolds)
UFH 1 is about 50 metres and 2 litres per min
UFH2 is 3 loops of 80,80 and 50 each running at 2 litres per min
There are 3 pumps on my system
Main circulator plus each UFH manifold has its own pump
and d0 is set to 21 KW
Won’t be 1.42 lps as that’s 110kw at dt 20
21kw is 0.25lps / 15lpm at dt 20
Or at a dt 10 it’s 0.5lps
So 0.394 lps so 16.54kw the pump is moving
If all rads are producing their rated output then rad demand ~ 9.4kw.
UFH, 8LPM? at say a dT of 8C= 4.45kw. total, assuming no DHW = 13.85kw.
But, by calculation, boiler output at a flowrate of 1.42m3/hr @ dT of 12C, (70-58) is 19.82kw, 1.42x16.67x60x12/860, so again something not adding up, I suspect the pump is not now providing the correct data as one, its head at 3.7m can hardly even overcome the boiler Hx loss and two, by calc, the pump at those values is running at a efficiency of 54.85%, seems unlikely IMO, so again maybe reduce d.0 to a few kw below what your present calculated demand is, from pump flow&boiler dT and the flow temp should fall a bit below its SP, this will show up something.
I have gone through all of my radiators and their output is 9.4kw at Delta 50, 7.5kw at delta 40.
My underfloor heating has in total 7 loops manifold 1 and 6 loops manifold 2. They are all configured for flow rate of circa 2 litres per second. I believe this gives 7.2kw with dT of 8 degrees, but they are probably running at 10.
Assuming I use delta 50 figure this gives me 16.6kw plus the hot water take - How to calculate that - 250 llitre tank, fully steel enclosed and cold to touch on outside.
My system if un vented, with the condensing boiler which is circa 2007.
I set the boiler to d0 21kw and it appears to be behaving better - Is this due to my load being no where near 30kw?
I have tried to balance the radiators with a 20 degree difference, although should it be 20 or lower?
Many Thanks for your continued responses and help
Andrew
Your load is 18kw you don’t add hot water re heat capacity in as you stagger your times eg an hour before the heating comes on the hot water comes on etc
I’m guessing the ufh is lpm so puts around 10kw at dt5 much better to run like this
You can balance the ufh as well with two clamp probes you want a difference of 5- 10 degrees so adjust the flow rate via the meters to sort this
Yes correct trying to shove 30kw down a 18kw load will cycling half the time roughly
Dt15-20 on the rads is good
Andrew
Your rads, with a 70C flowtemp & dT of 20C, output 7.03kw, 7.61kw at dT15C & 8.2kw at dT 10C.
Your UFH, if you have 7loops (UFH1) at 2LPM & dT8C will output 7.8kw & 6 loops (UFH2) at 2LPM&dT8C will output 6.7kw, total 14.5kw??.
If you run the rads alone at a dT of 20c then the boiler flow/return temps will be 70/50C. Boiler demand 7.03kw. flowrate 5.04LPM, 0.30m3/hr
If you run the rads+one UFH loop then the boiler flow/return temps will be 70/45C, dT 25C assuming manifold temp of 45C. Boiler Demand 14.83kw. flowrate 8.5LPM, 0.51m3/hr
If you run the rads+both UFH loops then the boiler flow/return temps will be 70/43C, dT27C assuming manifold temp of 45C. Boiler demand 21.53kw. flowrate 11.42LPM, 0.69m3/hr
DHW coil, if you run it alone then the boiler dT is the coil dT and use the pump flowrate and the calculation to get its output, can then add that to the others to see what comes up.
Going back to your original problem, is the boiler running better now because it reaches its SP of 70C before the dT reaches 14C or what?.
Can you clarify the above, has UFH1 got 7 loops flowing ~ 2LPM/loop, total 14LPM and has UFH2 got 6 loops flowing ~ 2LPM/loop., total 12LPM.
If so, then UFH1 output is 7.8kw and UFH2 output is 6.7kw.
You give a total output of 7.2kw which implies a total of ~ 7 loops?.
Sorry yes 13 loops in total @ 2LPM
If you run only one UFH then a boiler temp of 70C will result in a boiler flow of only 3.39LPM, 0.2m3/hr and a boiler dT of 33C which will probably cause the boiler to trip, if you reduce the boiler temp to 55C then the boiler flow is 6.21LPM,0.37m3/hr and a boiler dT of 18C. Running both UFH with boiler at 55C 55c will result in the same boiler dT of 18C & a flowrate of 11.55LPM,0.69m3/hr.
When you ran with rads+UFH1 can you remember the boiler flow/return temps and the (pump) flowrate?.
No, But I will take some measurements later. Thanks.
Is it likely that this is just a configuration / set up issue or boiler fault?
My engineer is coming back next week, but I am really not sure where to direct him and dont want to pay labour for nothing. I got the feeling when he was last here that he did not know where to look.
Hi Pretty much
Just fired up the CH, DWH off from relatively cold.
It seems to be cutting at dT of around 15 to 16 today
running at 3.2 head and 1.1 m3/hr
this was with d0 at 20
Dropped d0 to 10, but burner barely running and water not really heating
Guess I will need to get engineer back and have him call Glow worm for advice.
thx
Don't know if you made any progress but something strange (again).
If/when the rads only are on at 9.4kw then the dT should be ~ 7.4C at a flowrate of 1.1m3/hr so wonder if boiler sensors are OK even though you seem to prove that that they are/.
Not really, otherthan it works much better with d0 set at 21. Although concious that this is not enough power when everything is on and when it is cold.
Just tried now from cold (was at 28 degrees)
Boiler headed up to 70 and settled at
flow - 70
return 57
3.47 head
1.18 flow
I put temp probes on the flow and return into the boiler and the readings pretty much (<5 degrees) matched what d40 and d41 were saying.
I have my heating person coming back next week and have e-mailed glow worm who have given me a number for him to call and do some tests. I asked if I could do these tests etc, but was told that need specialist equipment?
Thanks again
Andrew
How fast did the return get to 57 ?
flow - 70
return 57
3.47 head
1.18 flow
Thanks again
Andrew
Did not time it, maybe 20-30 mins
flow - 70
return 57
3.47 head
1.18 flow
Thanks again
Andrew
< 5C might be significant if it resulted in your dT being 8C (13-5), this, assuming flow rate correct results in a heat demand of 11kw not a whole lot away from your rad demand assuming you didn't have the ufh or cylinder calling for heat.
Hope your heating person at least brings a multimeter with him/her to measure the flow/return sensors resistance and confirm them with Glowworm, probably did that at the last visit anyway.
Reply to Boiler Short Cycling in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net
I have an old Modena 80 E combi boiler that is randomly short cycling on windy days. The burner goes out and re-ignites within a few seconds and...
Hi Folks, I have a challenge with a Main Eco Elite 30 Combi which is short cycling on the CH. Water works fine. As soon as you have call for...
B
Issue with boiler short cycling in system with hot water tank. We have an ideal heating logic heat2 h15 boiler which feeds a hot water tank...
Good morning, wondered if anyone can advise please on a resolution? My set up at home is that I have a 4-bed detached with 21 radiators...
5K
Hi, Short version: Do frost protection valves trigger when the water in the pipe gets to threshold, or when the air temp drops? Long version...