Discuss boiler install gas pipe size in the USA area at PlumbersForums.net

I need a new boiler and would prefer a 35KW combi boiler but wanted to know if my existing gas pipe will allow it. I wanted to check this first so i can look at my boiler options before getting somebody around.
If you can find space for a hot water tank somewhere you could have a (much?) smaller boiler and the pipe capacity would no longer be an issue.
 
I would say unvented cylinder and a boiler if you have the space

if not could you go external with the gas pipe and back in close to the boiler ?
 
Sorry to say a 35kw boiler will need a new 28mm gas supply , you would be better to fit a unvented hot water cylinder paired with a new lower kw output boiler for a family home. Kop
 
I would say unvented cylinder and a boiler if you have the space

if not could you go external with the gas pipe and back in close to the boiler ?
Yes we looked at that as we can avoid going across the front of the house because the front room has carpet and suspended floor. But it would go the full length of our sideway and across the back. We have rendered walls with a black plinth along the bottom which is set back from the render 10mm so even if we tucked it under there it will stick out a fair amount, possibly 35/40mm.
Would look pretty ugly.
[automerge]1600508996[/automerge]
Sorry to say a 35kw boiler will need a new 28mm gas supply , you would be better to fit a unvented hot water cylinder paired with a new lower kw output boiler for a family home. Kop
The only place I have room for a cylinder is below the new wall hung boiler where the existing floor mounted boiler is but I'm not sure that would be enough space. I have attached a picture.
[automerge]1600510574[/automerge]
Thanks for all the advise, even though my original plan was for a smaller neater boiler perhaps I should go like for like and fit a direct replacement (greenstar 440 CDI high flow) which has a 7.5 - 29.2KW rating , I'm guessing that will work with my pipes.
Just trying to get my head around my best option before getting the engineer around . When you book an engineer through Bosch online you have to pick the boiler you want .
 

Attachments

  • MVIMG_20200919_104919.jpg
    MVIMG_20200919_104919.jpg
    97.6 KB · Views: 8
Last edited:
I need a new boiler and would prefer a 35KW combi boiler but wanted to know if my existing gas pipe will allow it. I wanted to check this first so i can look at my boiler options before getting somebody around.
I don't have any other gas appliances and my existing pipe is 22mm. The gas meter is located next to our front door in a box at ground level. I have no wish to take up my Oak floor to lay a new pipe.
I have attached a rough sketch of the gas pipe run and would appreciate any advise. Thanks .
Sorry to say a 35kw boiler will need a new 28mm gas supply , you would be better to fit a unvented hot water cylinder paired with a new lower kw output boiler for a family home. Kop
I you go up the wall just inside the wall with 28mm pipe at where meter is across in ceiling to where 22mm pipe where 10meter pipe is go half way on that pipe and join with reducer you have plenty of gas for 35kw boiler.
 
1. The range of the boiler is irrelevant I'm afraid. The testing must be done at full output, and your pipework will not cope with a 27 kW load.
2. As already stated, the absolute maximum your current pipework can support (subject to survey) is around 24 kW, and given the number of bends / elbows I suspect it won't really even support that.
3. If any of the long lengths on your diagram could have larger diameter pipes installed without major disruption, you might be able to upgrade those to 35 mm pipes and leave the remainder as 22. But this is a calculation which MUST be done by a Gas Safe Registered engineer who has full view of the site.
 
Is it possible for a gas Safe plumber to come around, open the gas pipe where the existing boiler is and actually take a pressure/flow reading so I know what I have exactly?
 
Is it possible for a Registered Gas Engineer to come around, open the gas pipe where the existing boiler is and actually take a pressure/flow reading so I know what I have exactly?

If the old boiler works, they can use it to get a ball park figure.

You need to measure the operating pressure.

Now saying that, I see very little benefit of the above if your diagram is correct. Pressure loses and acceptable pipe sizes can all be worked out with a calculator.

I’ve had to remove a 6 month old 30kw boiler before and replace it with a 12kw due to gas pressure issues.

The 12kw supplied a 160ish litre unvented cylinder, which in turn fed a one bed/bathroom flat. No issues with running out of hot water or heating.
 

Reply to boiler install gas pipe size in the USA area at PlumbersForums.net

Similar plumbing topics

It's not every day I deal with 110mm soil pipes, therefore I do not have a selection of different fittings at hand to try what combination fits my...
Replies
2
Views
435
I wish to add a second boiler to my existing meter. Location 20m away. Underground run. Can l use 32mm yellow pipe with copper tails at each end...
Replies
9
Views
481
I have decided to remove the timber floor boards and joists as they are effected by damp and rotting. Was hoping to infill and have slab and...
Replies
2
Views
356
Hi, I’m having a gas cooker pipe capped off. The GS registered plumber/ fitter, has told me that to do this, he’ll also have to service the combi...
Replies
3
Views
213
Hello All, I was hoping you could help with a potential boiler build query for my father. He has recently had a new boiler installed via British...
Replies
5
Views
253
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock