I need a new boiler and would prefer a 35KW combi boiler but wanted to know if my existing gas pipe will allow it. I wanted to check this first so i can look at my boiler options before getting somebody around.
I don't have any other gas appliances and my existing pipe is 22mm. The gas meter is located next to our front door in a box at ground level. I have no wish to take up my Oak floor to lay a new pipe.
I have attached a rough sketch of the gas pipe run and would appreciate any advise. Thanks .
 

Attachments

  • boiler 1.jpeg
    boiler 1.jpeg
    14.2 KB · Views: 37
1. Your gas run is roughly 20 metres.
2. You appear to have 7 elbows. I'd suggest you count this as 10 (allowing for ones by the meter which may have been missed), so a further equivalent 5 metres.
3. The manufacturer's data will tell you exactly, but a 35 kW boiler will require around 3.8 cubic metres of gas per hour.
4. A 25 metre run of 22 mm pipe will only support a flow rate of 2.6 m cubic metres / hour, so is inadequate.
5. Subject to a specific site survey, you would need 28 mm pipe for the run.
6. Because gas is compressible, a required flow rate may be achievable with a mixture of pipe sizes. This would need a precise on the spot calculation. It can't be done over the internet. However, it MIGHT allow you to avoid damaging a floor.
7. For those who might consider this too much information, all the above is freely available on the internet. Mostly at https://copperplumbing.org.uk/sites...achments/domestic-gas-planning-and-sizing.pdf
 
Gut feeling 28mm required as it’s around 20m

24kw is pushing it for 20m on 22mm
 
Ok thanks all. New pipe was my gut feeling but it's a real pain having to lift an oak floor and chase across a newly tiled kitchen floor.
I was looking at a 35k Worcester greenstar 8000 lifestyle as we have a Bosch Worcester floor mounted 400 high flow at the moment, the difference being the floor mounted has a hot water storage tank in it.
I have 5 bedrooms, one bathroom and one shower room and no other gas appliances so maybe a smaller KW would be ok. What do you think?
 

Reply to boiler install gas pipe size in the USA area at PlumbersForums.net

Similar plumbing topics

It's not every day I deal with 110mm soil pipes, therefore I do not have a selection of different fittings at hand to try what combination fits my...
Replies
2
Views
435
I wish to add a second boiler to my existing meter. Location 20m away. Underground run. Can l use 32mm yellow pipe with copper tails at each end...
Replies
9
Views
481
I have decided to remove the timber floor boards and joists as they are effected by damp and rotting. Was hoping to infill and have slab and...
Replies
2
Views
356
Hi, I’m having a gas cooker pipe capped off. The GS registered plumber/ fitter, has told me that to do this, he’ll also have to service the combi...
Replies
3
Views
213
Hello All, I was hoping you could help with a potential boiler build query for my father. He has recently had a new boiler installed via British...
Replies
5
Views
253
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock