I'm working on this boiler and the fault code is 30 and 50.

Ive cleaned the venturi out. Air pressure switch clicks on. Fan runs fine. Anything else I can check?

It works for a few days then fault appears again. I'm going back there now to check if the air pressure switch power if fine when the fan runs. Could it be the pcb?

Kind Regards
 
Yes ignites fine when resetting. Power to fan 230v. Power to air pressure switch 160v is that correct?
 
You may have a faulty fan, slowing down when bearing gets hot.
 
Yes think it might be the pcb. She reset it but I need to check resistance on the fan and continuity on the air pressure switch. I'll let you know what it is.
 
Yes think it might be the pcb. She reset it but I need to check resistance on the fan and continuity on the air pressure switch. I'll let you know what it is.

Buy a APS first,known to be weak ,especially so if its the square silver Honeywell type
 
Try moving/ skewing the Pcb when it's working , any dry joint loose connection will show up , have come across this a few times
 
Status
Not open for further replies.

Reply to Baxi combi 105he fault. in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi all I have a britony combi se 80 with fault 40 60 80 had british gas out to repair under homecare cover but they can't seem to repair it. They...
Replies
2
Views
389
Morco feb 24ed3 has a f1 fault code. The burner reading is fine. The fault is intermittent, sometimes the boiler won't ignite on either hot water...
Replies
0
Views
515
Conditions: nearly 10 year old boiler WB2B, heating mode off, DHW on or also in standby, Boiler shows no fault LED on, no new fault logged, room...
Replies
0
Views
413
Got up on Wednesday morning no hot water, (only cold water coming out of hot tap). Checked boiler, it had zero pressure and F1 fault showing. So I...
Replies
16
Views
1K
My Grant combi oil boiler is giving me quite a headache at the moment. When I returned home last Friday I'd no heating or hot water. An engineer...
Replies
3
Views
587
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock