Went to one the other day to service, noticed the hot water wasn't very hot. Didn't really have time to properly investigate but struggling to get more than about 8ltrs/min without it going tepid. B.P fine, not modulating or cutting out but heating flow didn't feel like it warmed up at all either, although the heating had been on before I got there. Any other ideas before I investigate further? Can only presume its creeping past down the heating slightly so only getting 80% or so to water.


cheers in advance
 
I had this once and I'm sure the problem was, it was just circulating round the by-pass ate the back, also this boiler uses the expansion vessel as a hot water storage.

ja7u6yqe.jpg


7ugybaty.jpg
 
I had this once and I'm sure the problem was, it was just circulating round the by-pass ate the back, also this boiler uses the expansion vessel as a hot water storage.

ja7u6yqe.jpg


7ugybaty.jpg

Is that the British gas software? I'd love to get my hands on that!
 
Looks like partsarena to me, i've got it on the works PDA and it is available as an app for ipad.
 
cheers doodle, makes sense, kind of. Surely the problem would be the valve rather than the pipe its self? Also, isn't it the instant which does that, and how does it do it, must be able to circulate the water in the vessel??
 
Looks like partsarena to me, i've got it on the works PDA and it is available as an app for ipad.
Bit more info on this laptop than partsareana.
Detailed fault finding, including step by step xsol. Also lists the common faults and how to test for them.
cheers doodle, makes sense, kind of. Surely the problem would be the valve rather than the pipe its self? Also, isn't it the instant which does that, and how does it do it, must be able to circulate the water in the vessel??
Correct. It is the piece of junk instant that stores the hot water.

Your issue initially sound like a blocked up Plate Hex. or a divertor issue or even a breaking down NTC.
Visit customer when there heating off to feel the flow and return pipes.
 
blocked hex would surely cause boiler to modulate, as would NTC?
 
Bit more info on this laptop than partsareana.
Detailed fault finding, including step by step xsol. Also lists the common faults and how to test for them.

Correct. It is the piece of junk instant that stores the hot water.

Your issue initially sound like a blocked up Plate Hex. or a divertor issue or even a breaking down NTC.
Visit customer when there heating off to feel the flow and return pipes.

xsol?
 
Looked all over the Internet for some disgruntled staff member getting rid of one. Sadly never found one!
 
Turn the return of with the isolater, if it works it's the divertor. If its modulating it's the ntc or hw hx. It won't be the bypass, there's no mechanical restriction. And they're all like that.
 
BG's pictorial, step by step, idiot proof, fault finding guide for a lot of individual boilers.
9 times out of 10 it gives you the answer you are looking for.
Oooooo I'd like to clone that hard drive....
Unfortunately the software is locked by some very good security software.

Just a thought. Did you check the basics by any chance?
Gas rate, BP, clean burner etc.
 
Yes, as first post, all good. Wouldn't have done a very good job at servicing it if the burner was dirty! :smilielol5:
 
BG's pictorial, step by step, idiot proof, fault finding guide for a lot of individual boilers.
9 times out of 10 it gives you the answer you are looking for.

Unfortunately the software is locked by some very good security software.

Just a thought. Did you check the basics by any chance?
Gas rate, BP, clean burner etc.

I know a man who can...
 
XSOL is a BPM tool. BG have probably built this up over time with their IP in their labs.
 
Bit more info on this laptop than partsareana.
Detailed fault finding, including step by step xsol. Also lists the common faults and how to test for them.

Correct. It is the piece of junk instant that stores the hot water.

Your issue initially sound like a blocked up Plate Hex. or a divertor issue or even a breaking down NTC.
Visit customer when there heating off to feel the flow and return pipes.

Yeh that's right, it's the instant that stores hot water. The diverted won't be passing, already stated in 1st post that heat isnt going into hearing so gotta assume this test was done with heating off. If the calorifier was block, it would modulate down and cycle on and off. :)
 
Just re-read, my apologies, as said above, isolate valve underneath or test with heating off.
 
I did turn the flow and return valves off whilst there to check divertor, nothing much changed but could have gone round the bypass?

It was all a bit hasty, as i got paid for a service not full diagnosis etc. I think I am more bothered about it than her, hence not going back, she just turns the tap down slower!
 
plate heat exchanger is blocked try taking it out and cleaning,as far as i know this 80 eco has no dhw ntc,some did though but the majority did not,if it does you should get 11k cold
 
Status
Not open for further replies.

Reply to Baxi 80 Eco in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi Folks, I have a challenge with a Main Eco Elite 30 Combi which is short cycling on the CH. Water works fine. As soon as you have call for heat, the boiler fires up, modulates, but jumps very quickly (about 30 seconds or so from 40'ish all the way to 70, burner disengages putting it the...
Replies
6
Views
378
M
Hello, We’ve recently moved into a fairly old, fairly big detached house (i.e. fairly draughty, but not too bad by any means) with a fairly new well maintained Worcester combi boiler. We weren’t convinced the heating was working right and then got hit with a £610 energy bill for the first 6...
Replies
0
Views
256
MartinPod81
M
Hello, my HW is taking longer than expected to heat up and it's getting worse. I can go 10-40 degs after 1.5 hours of only heating HW, whereas I should be going 10-60 degs in 30-40 mins by my maths. Don't even mention trying to heat HW and CH at the same time. 30 mins with the immersion adds...
Replies
2
Views
377
B
Issue with boiler short cycling in system with hot water tank. We have an ideal heating logic heat2 h15 boiler which feeds a hot water tank upstairs in the house. We have an issue where if the boiler isn’t set to 80c then the boiler will short cycle, the hot water tank thermostat is set at...
Replies
10
Views
1K
Hi everyone. I'm currently working on a job for a customer. their radiators are not all heating up. in total there is 12 radiators. 4 of these are on 15mm pipework, the rest are on 10mm. its powered by a Grundfos ups3 pump. the boiler is an 18kw heat only boiler. There are two radiators mainly...
Replies
1
Views
474
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock