Messages
6
Hi all, I have an issue with my UFH that I hope you can help with.

We have UFH but have never been 100% sure that it works as it should: the lounge/kitchen (one room) has been fine, but the bedrooms have always been a bit chilly. I've put this down to them being carpeted and it taking longer for the heat to transfer through.

But now we have a baby on the way and really need to get to the bottom of it, so I've been trying to adjust the flow valves to balance the rooms better thinking that this may solve the issue. However, when I loosen/tighten the flow valves only the one for the kitchen rises and falls to show more/less flow to that zone. Can anyone suggest what the issue may be? And is this tied to our flat being cold?

As an example, the heating was on all day yesterday and set at around 18 degrees in the bedroom. When we went to go to bed the thermometer was only reading 14 degrees.

Some additional info:
- The actuators all seem to work - the pins on top rise and fall in line with the thermostats in each room.
- I can tell that water is flowing to zones, even if the flow valve indicator is right at the top (0 l/s) because the pipes underneath feel hot. Likewise, when I close them all the way the pipes feel cold.
- The pump is brand new and was installed by a plumber due to the old one expiring.

Thanks in advance! Would appreciate any advice you can give me.

Here's what the manifold looks like:
IMG_20190123_221437.jpg
 
Doesn't look like it has been commissioned correctly.
The normal Flow temp would be 50 deg C you have 38-39 try adjusting the thermostatic mixer to raise the flow.
As it is cold & if the flow rates were correct I would expect to see around a 7 deg drop flow to return you have 1 or 2.
The high limit is set to 80 I would have expected 60 - 65.
 
Doesn't look like it has been commissioned correctly.
The normal Flow temp would be 50 deg C you have 38-39 try adjusting the thermostatic mixer to raise the flow.
As it is cold & if the flow rates were correct I would expect to see around a 7 deg drop flow to return you have 1 or 2.
The high limit is set to 80 I would have expected 60 - 65.

Thanks Chris,

I've just checked now and the flow is at 45 and the return is at 35 . I guess the high limit is the white box strapped to the front of the flow? I've turned that down to 60 as you suggest . It was the plumber who installed the pump that set all these temps, so guess I need a UFH expert next time!

Thanks again,
Chris
 
Thanks Chris,

I've just checked now and the flow is at 45 and the return is at 35 . I guess the high limit is the white box strapped to the front of the flow? I've turned that down to 60 as you suggest . It was the plumber who installed the pump that set all these temps, so guess I need a UFH expert next time!
Thanks again,
Chris
Do you know what is the mixing valve & how to adjust it to raise the flow temperature ?
Another photo of the pump etc to the left would be good.
 
Do you know what is the mixing valve & how to adjust it to raise the flow temperature ?
Another photo of the pump etc to the left would be good.

Here you go - sorry everything looks a bit dusty!

IMG_20190124_223018.jpg


I believe the mixing valve is the white plastic thing in the top of the picture (set to 45 degrees), which will take the water from the boiler (circa 80 degrees) and mix it with the return from the manifold (c. 35 degrees) to get the right temp for the UFH?

Is 45 degrees about right for this? I understand it shouldn't be too high as the floor/pipes/fittings might not like it?

Thanks again for any help on this - my wife and I really appreciate it.

Chris
 
Hi Chris & Wife
The normal flow temp for these system is 50 degC so I would suggest you turn it up a touch (don't tell anyone but at a push it could go up to 55- 60 but no higher).
I would also suggest turning the pump down you have a small system & the new pump is more powerful than the old, push the button next to the green speed light indicator until "I" is illuminated (not flushing).
Try that & see, otherwise it is either the length of time it is on for (it takes the heating an hour to raise the room temp by 2degC) or flow rates need adjustment.
PS. wish you both well with the new baby, is it your first??
 
Hi Chris & Wife
The normal flow temp for these system is 50 degC so I would suggest you turn it up a touch (don't tell anyone but at a push it could go up to 55- 60 but no higher).
I would also suggest turning the pump down you have a small system & the new pump is more powerful than the old, push the button next to the green speed light indicator until "I" is illuminated (not flushing).
Try that & see, otherwise it is either the length of time it is on for (it takes the heating an hour to raise the room temp by 2degC) or flow rates need adjustment.
PS. wish you both well with the new baby, is it your first??

Thanks Chris, yes it will be our first. The pump is on setting 2 out of 3 currently, so I'll turn it down to 1, and also bump the mixer up to 50. We have the heating on almost permanently as it seems so ineffective, so it can't be to do with that.

If it still doesn't work I'll call in a pro to bleed it and balance it.

Thanks again,
Chris
 

Reply to UFH problem: flow valves not rising and falling in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
100
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
117
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
240
I have had a look at previous posts and think I know the answer to this but just before I make it worse could I just check what you think about this one. Granddaughter just moved house and this valve decided to leak when it was closed. When open its fine. Normally I have repacked the gland on...
Replies
7
Views
181
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...