One of these yellow tags

Screenshot_20181219-121823_WhatsApp.jpg


Screenshot_20181219-121823_WhatsApp.jpg
 
Board left of solenoid
 
There you go mip 75 mbar

Mop 23

So test would be 82.3 so 83mbar so you could test the mdpe at 100 mbar
 
There you go mip 75 mbar

Mop 23

So test would be 82.3 so 83mbar so you could test the mdpe at 100 mbar


Thanks for the calculations. As I don't have a gauge that does 100mb, I could do this as you suggested in the 1st place to 1 bar as it is only a soundness test after all. But, as you say it is commercial so should I avoid.

Well if one thing that comes out of this I have learnt a bit about cost of fittings for this size pipe and strength testing.

Thank you all
 
Upto you as it's not connected you could say your only testing the pipe for defective not carrying gas
 
Don't have one

Got a dial gauge eg pressure and an anton 140
 
Bes do a 100 mbar gauge

IMG_3950.JPG
 
So went to pressure test this job but the pipe was not installed to regs. They had run yellow mdpe into the building which if I remember correctly is a no.

I do know the gas board do this though when replacing the mains to the meter inside the house with mdpe by pushing it up the old pipe.
 
So went to pressure test this job but the pipe was not installed to regs. They had run yellow mdpe into the building which if I remember correctly is a no.

I do know the gas board do this though when replacing the mains to the meter inside the house with mdpe by pushing it up the old pipe.
Any pics?
 
into the building is ok under the building no no
 

Reply to Pressure testing 63mm gas pipe in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
114
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
445
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
186
I have had a look at previous posts and think I know the answer to this but just before I make it worse could I just check what you think about this one. Granddaughter just moved house and this valve decided to leak when it was closed. When open its fine. Normally I have repacked the gland on...
Replies
7
Views
184
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
231
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock