Hi all!

Sorry if this has been asked before but i haven't been able to find anything out there...

We made our CH system zoned when I laid some UFH in the kitchen. (2 zones total: kitchen + rest of house) each zone has a Honeywell 2-port zone valve. The boiler is a Glowworm combi.

All is well with the system *except* when the heating isnt running and the system cools down. When this happens the pressure drops. HOWEVER if manually open one pf the honeywells the pressure instantly is fixed and returns to the normal 1.0 bar. For this reason I'mm 99% certain there isn't a leak in the system (pipes were all replaced 18 months ago)

I recently installed an auto-bypass valve thinking that this was the culprit. However, no matter what setting i change that to, the problem remains.

Any help greatly appreciated, if you need any further info do ask!

Cheers,
Paul
 
Hi Scott, thanks for your reply!

No I didn't add an expansion vessel, but yes there is a manifold for the UFH. Have added some pictures (it's still a work in progress as you can see! Sparky will sort cabling when he does 2nd fix)

Thanks,
Paul
 
Hi @scott_d here are the pics I mentioned earlier. the combi boiler is just above, out of shot, if you need any more info do just ask, thanks again!

Paul

IMG_20190219_092242.jpg


IMG_20190219_092354.jpg
 
Yeah I know! I think a pro may be called in to put in some copper to neaten everything up, but in an effort to minimise exlense I've installed the UFH myself (also found it v difficult to actually get quotes for installation: no-one seemed to want to do it)

The UFH is a single run of 50metres. There are 7 rads in the house and the boiler is a Glowworm Easicom 24...

Thanks again,
Paul
 
Hi @scott_d @Riley just following up this thread again... So do you think the expansion vessel in the combi itself has died, or does the system now need a second EV because I've turned it into a zoned system? I'll have a look and see if there's any pressure in the internal expansion vessel if you think that's a good idea.

Will have time to fix that PRV today too!

Thanks
P
 
If system volume has increased then a larger expansion vessel must be calculated for and installed to accommodate the larger volume. If an expansion vessel is too small, lost some charge, lost all charge or charged too much then you should expect PRV discharge and as said above this dripping on any electrics can cause problems.
 

Reply to zoned system, pressure drops when cold (but goes back to normal when i manually open valve) in the Plumbing Zone area at PlumbersForums.net

Similar plumbing topics

A bit of clarification - I have extended a 3 bedroom semi detached and at the time central heating pipes were going in I told the plumber could I...
Replies
0
Views
480
Hi. This UFH system is in my mil's bungalow purchased earlier this year. It has 9 zones, is run from a WB 37CDi combi, and uses Wavin actuators...
Replies
7
Views
1K
Hi I have a 4 zone / 7 loop UFH system. 2 zones (4 loops) always get hot when the system is on when the zone thermostats and actuators are...
Replies
14
Views
1K
I have a Vaillant eco plus 837, year installed 2008. It works well. We have one large zone for the house with 13 rads running off it. We also...
Replies
1
Views
337
So I have a combi boiler with a hive hooked up to it and from what I can tell its a Y plan(I think) with 1 zone. So I crank up the heat on the...
Replies
13
Views
2K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock