Worst corrosion I've seen yet..

Discuss Worst corrosion I've seen yet.. in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.

Anders0n

Plumbers Arms member
Plumber
Gas Engineer
Messages
37
Had to replace a 3 port, refilled the system and the boiler kept over heating and locking out.

Thought it was an air lock, tried to clear it for hours before deciding to take the pump off...

2qunes0.jpg


28mh1uc.jpg


That explains that then
 
Seen similar corrosion with what seemed a clean open vented system. Pump acts as a magnet. Better a sealed system when possible.
 
Needs a power flush!

Ha try getting this customer to pay for that!

System is massively corroded. Cold feed and Vent are in completely the wrong places causing constant pumping over into the header tank.

Oxygenated water constantly being drawn in, nice.
 
That explains it! Entire system is probably for scrap.
 
Ha try getting this customer to pay for that!

System is massively corroded. Cold feed and Vent are in completely the wrong places causing constant pumping over into the header tank.

Oxygenated water constantly being drawn in, nice.

Its not a case of trying to get them to pay for that.
That is your diagnoses if they don't accept it, charge them and move on.
 
seen them this bad plenty of times the only fix is to cut out and replace
 
Ring Magnaclean or Fernox and tell them you have a great system for a case study on, if its that full of sludge theyll probably give you a filter for free just for the publicity
 