Discuss working pressure at meter in the Plumbing Jobs | The Job-board area at PlumbersForums.net
The fact is it should be 19mlb min but if you make the call to get them to come and change thye gov. they may refuse as petty to them. Providing no appliances are effected and all burner and working presures are achieved dont worry about it..thats just my oppinion...
Bren.
Am I right in my understanding that if working pressure if lower than the say 19mbar at meter, 18mbar at appliance, it will not affect the flow rate of gas available to the appliance? i.e 3m of 15mm pipe can supply 2.9m3/hr with a 1mbar drop. If length was longer (say WP showing a 2mbar drop) then 2.9m3/hr could still be delivered to the appliance?
It depends on the appliance but i dont know of one that it would affect,, AS PER VOKERA they have domestic modles that a dynamic gas presure as low as 12mlbr,, yes 12mlb is ok and wont affect its opperation..but thats only vokera, VAILLANT have told me they need 15mlb to opperate ok and 18mlb on WORCESTER..ITS DOWN TO THE MANUFACTURER...
Bren.
it depends on the type of appliance, hobs/cooker and gas fires normally rely on the correct pressures to operate correctly.
if the gas supply is not right you wont get the right flow rate and temperature from a combi. regardless of any manometer imho
but if calculated pipe size is ok, gas rate is not adjustable (zero govenor), OP inlet pressure is within spec, and gas rate within 10% of MI would you accept this gas rate as being close enough as acceptable
Sorry i was thinking standing pressure Between 19-30mb. Working Pressure 21 +or- 2mb
Call out transco for new governer.
Reply to working pressure at meter in the Plumbing Jobs | The Job-board area at PlumbersForums.net
I have a green star ten yrs old keeps increasing pressure, feel on off filling valve not working, drain off to recommended, but after few days it's increased whilst cold...is this a regular problem.
Can anyone remember the Mira mixer shower that would work down to a really low pressure on a vented hot water system without a shower pump?
Can anyone recommend a decent multi meter, preferably under a 100 pounds. It's for checking boiler components so I don't need a top spec one ....just easy to use and reliable. The fluke 115 looks good but its above my budget. My current socket and see one was great but it's developed a fault.
