Hi guys

Does the worcester cdi have an internal bypass?

Long story short ive done some ufh on a worcester cdi not a big system 7 rads and ive added a 10m2 conservatory pack.

Both zone valves ( for ufh and radiators ) have been left locked open untill spark goes back. Just over a week later boiler developed EA fault and goes to lockout after 4 attempts sometimes it lights briefly.

Customer has got boiler cover so they have been out. First said the condense was blocked. Then something else. Now they saying its pressure build up as i havnt fitted a bypass.

Just want to double check before i tell him hes wrong
 
Have you split the system into a s + plan ?
 
Needs an external bypass as the internal one won't cope

Are / have they been locked open when the fault is on ?

But they shouldn't cause an issue as ea is normally no flame detected
 
Needs an external bypass as the internal one won't cope

Are / have they been locked open when the fault is on ?

But they shouldn't cause an issue as ea is normally no flame detected

Yes both locked open with fault on. Boiler goes stright to lockout so i cant see how it would be pressure build up anyway
 
I had one recently where the tube inside the condense trap had kinked and was causing the condense to back up. Worcester have completely changed the trap now. It is nothing like the original design. Not done it once since.
 
May not have an integral bypass if its a CDi conventional.
 
Status
Not open for further replies.

Reply to Worcester cdi EA fault in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello, My mum has a Worcester Greenstar HE30 boiler (15+ years old). Since its last service (and possibly coincidentally) it has been making a...
Replies
8
Views
2K
    • Like
Hi Can anyone help? I've got a problem with an intermittent EA fault on a Worcester Greenstar 38CDi Classic GC 47-406-38. I was called out to it...
Replies
2
Views
3K
P
Hi there, please help dont have a clue how to set this up. Ive recently installed a complete new central heating system in my house myself. The...
Replies
22
Views
3K
Hi everyone Other posts on secondary circulating pumps have been partially useful but grateful for any guidance on the following: S-plan system...
Replies
2
Views
2K
Evening all, first time poster here. I have a Worcester Bosch Heatslave 18/25 ext boiler. It’s been working fine as of late, however, yesterday...
Replies
17
Views
4K

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock