Discuss worcester 28i junior gas rate in the Plumbing Jobs | The Job-board area at PlumbersForums.net
C
coley
gas rate 2.7 m3/hr on high fire MI states 3.02 m3/hr. Working pressure 20 mbar.
readings from anaylizer
co2 9.8
02 3.6
x air 20.8
co ppm 100
CO/C0 0.0010
On low fire all readings as per MI
Whats the problem
Any help please
Thanks Coley
Thanks for that I did a search but I did not search hard enough. Its the very same problem I have come across. However the ratio is higher.
We have spoken to worcester regarding this and they said it was a blockage in the gas valve and are sending an engineer out.
After reading the other post I dont think this is the case.
Another problem is the hot water delivery the boiler can not keep up with demand. Which I thought was linked to the low gas rate.
Mcws is approx 6.5 bar
dhw 8 ltr per min =approx 45c to 49c to be honest its all over the place
drop it down lower say 4ltr per min and it can achieve about 55c
To compare like for like is that normal for the 28i junior.
gas rate =90@2mins = 28.86Kw gross, 26.24Kw net
Coley
If worcester are sending out an engineer then leave it at that. Your readings are good.
As far as your hot water is concerned the temperature your getting sounds ok to me based on the fact that the boiler will have a temperature rise of >30c or >35c, so based on incoming mains temperature (lets say 8degreesC) you are exceeding that at 45c.
What was the gas rate in net KW? Isn't the 3.02 m3/hr that you stated used for working out pipe sizing?
So your just over your 5% tolerance. Have you checked pipe sizing and standing pressure at meter and inlet pressure (1mbar drop across pipework) If thats all good then wait to see what worcester say and please report back to let us all know if it turns out to be a problem with gas valve.
Worcester have been on site apparently all I know until Monday they have changed a part I presume the gas valve. I will not know until Monday. But will post back. Thanks for the help
Regards Coley
Speaking to a fellow gas engineer this morning at the merchants who mentioned he had a problem with a brand new worcester 28i boiler that fired up first time and then wouldnt fire again. He spoke to worcester and they told him that there was a problem with some gas valves that were leaving the factory without being set up properly. Apparently to the top right of the valve there is a 2.5mm hex srew covered in that red wax (not apparently were you adjust your gas/air ratio) and these can be clogged with the red wax. Allegedly if you wind this right in till it stops and then unwind 2 1/2 times (possibly 3) this will set up the gas valve and clear any red wax blocking it. Might be worth keeping this info in back of mind in case we come across this issue again and try it.
Coley
:eek: never had one fail in the past , i will look out for that.
Could also just be the meter giving a false reading. I have come across some where the first half of a measured volume takes a completely different amount of time to the second half!
Dont forget that when taking your readings from the test point on the gas valve, i.e for resistance across the pipework,there is a resistance of 2mbar across the valve, so to confirm that i have only a 1mbar drop across the pipe work ,i cut in a test nipple on the supply underneath the boiler and test from there .
its very unlikey you will get a false reading from the meter .
'unlikely' and 'impossible' are not the same word. I can think of no other explanation as to why a meter would consistently give different timings for two halves of a measured volume than there being some meter fault.
worked at bg for 20 years and we supply the meters ,they do not go wrong.
the person reading it doesnt have a clue what there doing thats whats wrong
Meters do read the same amount of gas at different rates thats why the test is done over 2 minutes, down to the way the bellows work inside the meter.
Reply to worcester 28i junior gas rate in the Plumbing Jobs | The Job-board area at PlumbersForums.net
J
  • Locked
Hello guys I have a Worcester 28i central heating system. Yesterday I came home to find the house was freezing with no central heating and...
8K
G
  • Locked
Situation:- Service to Worcester Greenstar 28i Junior. All good as far as CO2% (9.8 Max 9.2 Min), condense trap cleaned, flue and terminal good...
5K
JBP Heating
J
  • Locked
My central heating is making strange noises (and it isn’t turned on) and I’m hoping someone out there can help me work out what is going on...
2K
diesel_ltd
H
  • Locked
Hi, i just wanted to know if any 1 has any ideas about why the hot water comes out ok in my kitchen sink downstairs but upstairs in my bathroom my...
3K
  • Locked
I serviced a boiler the otherday and they client then asked me to look at their business boiler as not worked for about 6 months. She said she had...
12K
professorplumb