then if all else is ok it must be the bath taps. can you put your temp sensor on the hot flow from the boiler and watch that
I completely agree with you from what I can tell the boiler works perfectly albeit is the Biasi
 
Yeah and the boiler continues to fire. It’s almost as if the hot water is diverting elsewhere but it’s not
The heat must be going somewhere. Are you sure the rads aren't getting hot (whether you want them to or not) when the hot runs cold? Might be problem with the 3-port valve in the boiler. I would switch it to hot water only mode and see if it happens, and if the boiler continues to fire if it does.
My son has a combi (Vaillant if I remember right) which was behaving oddly, not unlike your symptoms. They said it was an uncommon but known fault, and replaced the valve under warranty. Been OK since.
 
I went back last week the radiators are categorically not getting hot. I have quoted for new taps
 
I went back last week the radiators are categorically not getting hot. I have quoted for new taps

I wake up in the middle of the night thinking about this one, make sure you report back lol
If its the taps I will show my arse on the townhall steps.
 
Sounds like you have discovered a new law of thermodynamics :p
Ha ha perhaps I have, the only thing changed there is the taps, from speaking to the last tenant there was never a problem since they’ve put these ones on with a much greater flow there has been a problem. There’s no other logic to it unfortunately
 
Right, update. Changed to quarter turn pillar bath mixer tap maximum 9 lpm maximum and the problem has gone. I cannot see what the reduced lpm would have done but it seems to have done the trick.
Thanks all for your thoughts it remains a head scratcher
 
Right, update. Changed to quarter turn pillar bath mixer tap maximum 9 lpm maximum and the problem has gone. I cannot see what the reduced lpm would have done but it seems to have done the trick.
Thanks all for your thoughts it remains a head scratcher
Not for the first time, I was wrong! Good that you've cracked it.
 
Right, update. Changed to quarter turn pillar bath mixer tap maximum 9 lpm maximum and the problem has gone. I cannot see what the reduced lpm would have done but it seems to have done the trick.
Thanks all for your thoughts it remains a head scratcher
You are welcome mate. Taps are a weird thing sometimes.
 
24kw boiler ?
 
Good point well made but boiler is literally only 9 months old. I mean it could be shot but......
 
Might be worth a shout to the manufacturer
 
As I say though mate doesn’t affect any other outlet. Kitchen sink buckets out hot, basin buckets out hot. LL didn’t want floors up to check pipework etc so taps was his cheap fix. As I say just a mystery that hot would just cut out from the tap after 10-15 mins
 
As I say though mate doesn’t affect any other outlet. Kitchen sink buckets out hot, basin buckets out hot. LL didn’t want floors up to check pipework etc so taps was his cheap fix. As I say just a mystery that hot would just cut out from the tap after 10-15 mins

It's one of those pita faults :D
 
Always the same prob the letting has stated a price to the ll:D
 
Still we don't really understand where the heat was going though. The not-a-mixer-tap was not receiving hot water, yet the boiler was firing without boiling/exploding/overheating and locking out. Yet it's not your problem now :) at least.
 
Status
Not open for further replies.

Reply to Weird hot water issue in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Evening All, Been having on and off issues with a Greenstar CDI classic Combi were the hot water is not heating up but only intermittently. Some...
Replies
2
Views
509
Hoping somebody can help, So, in a nutshell… Standard 90s Westbury home – condensing boiler, pump, wall thermostat, etc etc... Normal, common or...
Replies
8
Views
598
Hi, I am probably being unduly paranoid here but I noticed under our kitchen sink that there is some corrosion evident on a small section of...
Replies
9
Views
300
Looking for any ideas to help. I've a Heatrae Sadia Hot Water tank, heated through Oil fired boiler (working fine). A week ago I reset the air...
Replies
8
Views
345
Hi, I'm new to the forum and just some background on myself. I have 4 years experience as a plumber but haven't worked in the trade in 15 years. I...
Replies
13
Views
633
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock