Hi Lads/lasses just wanted some advice on unvented cylinder inspection. I just took on what seems to be a contract for a block of flats all with direct heating via immersion. The way they have been installed seems a bit off as there is no check valve on the supply to the cylinder. It goes,
Stop tap
Double Check valve
PRV
then tee's off to the cylinder feed and cold water supply for the rest of the apartment.
When draining i noticed if i opened up a cold tap downstairs and opened the TPRV hot water came out the cold tap.
I explained to the customer what's going on and she said she has noticed she has to draw off a bit of hot water out the cold tap before filling a glass of water and thought it was normal.
The cylinders haver been installed in 2004 was the water regs different then? as they didn't require a DCV?
Can i carry out a cylinder safety inspection in this current state?
I have only been doing unvented for around 6 months now so I'm still getting to grips with the certs. I have a picture but my phone won't upload as of yet.
 
Hi Lads/lasses just wanted some advice on unvented cylinder inspection. I just took on what seems to be a contract for a block of flats all with direct heating via immersion. The way they have been installed seems a bit off as there is no check valve on the supply to the cylinder. It goes,
Stop tap
Double Check valve
PRV
then tee's off to the cylinder feed and cold water supply for the rest of the apartment.
When draining i noticed if i opened up a cold tap downstairs and opened the TPRV hot water came out the cold tap.
I explained to the customer what's going on and she said she has noticed she has to draw off a bit of hot water out the cold tap before filling a glass of water and thought it was normal.
The cylinders haver been installed in 2004 was the water regs different then? as they didn't require a DCV?
Can i carry out a cylinder safety inspection in this current state?
I have only been doing unvented for around 6 months now so I'm still getting to grips with the certs. I have a picture but my phone won't upload as of yet.
You cannot put a valve between cylinder and one of the pressure releif valves, and yes the way it is configured the water will syphon down cold if the supply to cylinderis isolated and you open TPRV.
 
Cheers Ricky. Its an Albion stainless steel no fitting instructions and none on the web to be found. So as it breaches water regs because its allowing hot water to mix with potable water, legionella and all that i guess i cannot sign off the inspection report. I just wanted to know if the regs changed from 2004 till now because it looks like 250 apartments are piped up wrong?
 
You can see the gate valve at the bottom of the cylinder feed a pipe goes through the floor. this is the cold feed to the kitchen and bathroom
 

Attachments

  • Resized_20210304_163659.jpg
    Resized_20210304_163659.jpg
    155 KB · Views: 37
So when expansion is taking place it expands into the cold and then into the expansion relief valve as the expansion vessel was flat as a pancake and has not had a service since it was installed.
 
Ok i got hold of kingspan that bought Albion cylinders so thanks Scott D for the hint. They have been plumbed up incorrectly as they should have a on return valve protecting the cold feed to the apartment even back in 2004. I ow have the pleasure of changing around 200+ cylinders ;)
 
I would think it’s acceptable as it’s not really different than installing the inlet block on the cold water mains and having the cylinder upstairs in the airing cupboard

you might have a check valve passing on a tap or shower ?
 

Reply to Unvented cylinder inspection in the USA area at PlumbersForums.net

Similar plumbing topics

Hi, I'm in my new build 2 years and the shower pump has died. I have an air to water unit downstairs is in the utility which I've been told is...
Replies
6
Views
253
Good evening, I'd like your opinion on something that is worrying me please: my landlady's plumber replaced the bottom/night element of my...
Replies
2
Views
487
S
Hi All I had an unvented cylinder fitted about 6 years ago. It only supplies hot water to my shower. I was hoping for a much better flow rate from...
Replies
2
Views
551
Steveo111
S
  • Question
Hello, I am fitting new taps and a shower mixer in my en-suite and was looking to isolate the hot water pipes. I have an unvented indirect...
Replies
2
Views
652
Hi There was no shut off valve on the tank feed to the hot water cylinder, and I needed to move a couple of hot water pipes, so I shut off the...
Replies
4
Views
258
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock