Hi everyone,

Been to look at a Thorn Apollo tonight, 30/50b. The pilot will light if I hold in the gas valve button and press the ignition button but goes out as soon as the valve button is released, holding it in long enough but it doesn't want to know.

Thermocouple looks ropey.

Have tried lighting lots of times according to instructions but makes no difference.

I'm thinking thermocouple, is there anything else it could be?

Thanks
 
Thermo or gas valve most likely thermo normally bell on the end if fecked
 
Thanks, I actually said thermo or gas valve to cust. Will give price in the morning.
 
I dont know the boiler but just check the pilot jet is not full of ****
 
I'd change the overheat stat and leads at the same time as the t/c, can also be the gas valve (normally a green button so very old). Go down the thermocouple and o/h stat rout first, then tell them to get rid of the old boiler!!!
 
Good shout about the overheat stat, think it interrupts the thermocouple. I haven't seen one of these boilers in a few years though
 
Good shout about the overheat stat, think it interrupts the thermocouple. I haven't seen one of these boilers in a few years though
Yup, good in their time but need to be in the bin now...... Had a massive shock off of one once when I bridged out the pump stat with the back of my hand!!!
 
Apologies for the delay in updating, the job was postponed while the cust went away.

Ok I replaced the thermocouple yesterday, relit the boiler no problem, turned the stat up boiler fires. Waited for CH to start circulating. All fine, went on my way. Had a phone call boiler has gone out same day and won't relight.

O/h stat?
 
If the over run stat is not working, the residual heat can cause the HLS to knock the pilot out.
If the Boiler stat is out of calibration or not working, that can do the same.
Both can be tested.
 
I'm going to have to pick parts up again, would I be correct in thinking I shouldn't need the gas valve?
 
Sometimes the old gas valve gets a bit sticky, just try flicking the green button a few times then relight but hold button in for a bit longer .
 
Thanks for the reply.

It's the gas valve with the round grey button.

I'm confused as the boiler would not stay alight at all. I could get the pilot to light but would go out straight away once valve button released.

Changed thermocouple, pilot lit as it should, stayed on as it should. Boiler fired up fine with heating demand, rads got hot. Then I got a phone call saying the boiler had gone out same day and cust can't relight. Going back Friday. Need to have it sorted.
 
Thanks for the reply.

It's the gas valve with the round grey button.

I'm confused as the boiler would not stay alight at all. I could get the pilot to light but would go out straight away once valve button released.

Changed thermocouple, pilot lit as it should, stayed on as it should. Boiler fired up fine with heating demand, rads got hot. Then I got a phone call saying the boiler had gone out same day and cust can't relight. Going back Friday. Need to have it sorted.
Do the same have had this fault with the Honeywell valve , have one that I service every year, takes a wile for pilot to stay on just hold the button in for longer, Try removing button give it a squirt with WD and push it in a few times, common valve loads around
 
Thanks for the reply.

It's the gas valve with the round grey button.

I'm confused as the boiler would not stay alight at all. I could get the pilot to light but would go out straight away once valve button released.

Changed thermocouple, pilot lit as it should, stayed on as it should. Boiler fired up fine with heating demand, rads got hot. Then I got a phone call saying the boiler had gone out same day and cust can't relight. Going back Friday. Need to have it sorted.
Did he thermocouple have an interrupter or not?
 
Status
Not open for further replies.

Reply to Thorn Apollo, pilot will not light in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I have a 40 year old floor standing Glow Worm 45-60 boiler (open vent )which is in a cupboard in the centre of the house. Its an old workhouse...
Replies
2
Views
364
Hi, Am trying to understand my mother's Apollo boiler. It has an intermittent fault. In the last couple of years, it has had a new...
Replies
4
Views
857
  • Locked
I have a 40 year old Glowworm Hideaway 100. I have lived in this house for 8 years and it has been faultless, until recently. The pilot light...
Replies
20
Views
5K
Hi, Can I pick your brains? My boiler is often reluctant to start, sometimes it does, sometimes it seems that it will if the demand is from the...
Replies
19
Views
1K
Hello I'm seeking helpwith a central heating problem please. It's a fully pumped system with a diverter valve for cylinder / rads and has an open...
Replies
1
Views
1K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock