Discuss Switching from Gravity to fully pumped - open vent position? in the Central Heating Forum area at PlumbersForums.net

Messages
3
Hi, Our gravity HW tank split and without a long delay the only one we could get was a fully pumped tank. Fairly easy replumb to get the tank in, however on all diagrams I've looked at, the fully pumped system has the open vent coming off between the boiler and the pump, whereas in our current gravity install, the open vent comes off the connector at the top of the coil.

Are there any specific requirements of where to put the open vent when moving to fully pumped? The pump is very close to the boiler so will be a bit awkward to "T" in to the pipe between boiler and pump. I've attached a before / after - is the vent pipe new position okay, or do I even need to move it there?
 

Attachments

  • Heating-setup-pipework.jpg
    Heating-setup-pipework.jpg
    36.7 KB · Views: 25
Last edited:
To comply with current building regulations the system should be fully pumped, although there are still many systems like yours out there. If you’re going to make the system fully pumped (which I advise you do for a number of reasons) then you’re going to need to reroute the cold feed and vent, you will also need either two 2 port valves or a 3 port, diverter or mid position. The system will need to be rewired as well. I would advise on having someone else carry out the work.
 
The recommended way (below) is Boiler, Vent, cold feed, Pump. (VCP). this sometimes also gives problems but if you tee the cold feed directly into the vent right at the header tank, preferably also in 22mm pipe then a almost 100% guarantee of no problems. (See mine, 50 years).



1646219116435.png


1646218845909.png
 

Attachments

  • Combined Cold Feed & Vent. rev1.JPG
    Combined Cold Feed & Vent. rev1.JPG
    36.9 KB · Views: 20
Easier to low pressure seal it eg 0.5 bar as they always pump over as the feed and vent are in the wrong position
 
Or leave it Gravity.

Replaced many old gravity cylinders with one's that are meant to be only fully pumped with no issues in the past.
If leaving gravity the system should at least be wired as a C plan. That way there is no constant cycling at the boiler during a HW on period at the programmer and cylinder at temperature
 
If leaving gravity the system should at least be wired as a C plan. That way there is no constant cycling at the boiler during a HW on period at the programmer and cylinder at temperature
Why? It would just be like previous on the boiler stat.

In agreement that, yes it would be better and very much more energy efficient. But there's many systems like this, and I would only see the need in upgrading controls etc. if replacing the boiler. But there's no requirement when replacing the cylinder in my eyes.
 
That’s exactly why the C plan valve was designed. To prevent boiler cycling and save fuel. If someone doesn’t want that then that’s on them but a no brainier in my eyes.
 
There was a post or two on here about someone who replaced the gravity cylinder with one that allegedly would work likewise but couldn't produce a drop of hot water seemingly because it had a corrugated coil.
 

Reply to Switching from Gravity to fully pumped - open vent position? in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

I have had a look at previous posts and think I know the answer to this but just before I make it worse could I just check what you think about...
Replies
7
Views
257

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock