Stick boiler on the e setting and that's it. If it's open vent check all your pipe work is lagged and your headder well insulated.

Is the pump wired directly to the boiler? If not ask your installer to come and correct this as it will immediately invalidate your warranty. Take it you don't have an Eco pump? I would look at a filter, smart start stat and check your cylinder stat isn't set above 70c .
 
Hi Deester u say u have the boiler stat at 2 then like simon said turn up stat. Is what ever your measuring temp with accurate. ?
 
Is the boiler set up correctly by a gsr fitter
 
Soz wot i ment to say was when the boiler was installed was it set up correctly . ie gas pipe sizing , combustion analysis and gas rated?
 
OK so two things found. Firstly the flow rate WAS too high. I slowed the pump back to setting 2 and I can now open the radiator lock shields more and still achieve a decent differential. I settled for 10-15 deg c as each lap around the house gave slightly different readings as I adjusted each rad in turn.
Another thing I noticed was that I was getting hot water with just the heating on. I hadn't noticed this before because because the programmer was set to heat water. I tried the hot water without heating and found the radiators heating up. I found the cause of this to be a faulty diverter valve. I am wondering if this could be the cause of high bills. Boiler heating both systems when only 1 was needed?
All in all I now seem to have a nicely working heating system and its much quieter too. No more slurping and gurgling noises.

Thanks for all the help!
 
Status
Not open for further replies.

Reply to Some questions about balancing central heating in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, I have a Worcester 28i junior boiler that has started to lose pressure, only when using the central heating. When using hot water I have no...
Replies
6
Views
277
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
292
PSxxxxxx
P
I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler...
Replies
1
Views
196
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer...
Replies
4
Views
291
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
227
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock