Discuss Solar Thermal Cylinder Installation in the Renewables area at PlumbersForums.net

D1 is rising
T and p has been altered from manufacturers spec
No tundish
D1 is too long
D2 is incorrectly sized
2 port is inaccessible
Pump is inaccessible

just to name a few
 
Thanks, could you clarify which bit you are referring to - so that I know exactly what I will be referring to when go back to them (and perhaps Gas Safe to make sure they were G3 qualified). Thanks for your input.

As much as you don't want hear it my friend almost everything in the picture from what I can see is non compliant, or against standard procedure.
 
D1 is rising
T and p has been altered from manufacturers spec
No tundish
D1 is too long
D2 is incorrectly sized
2 port is inaccessible
Pump is inaccessible

just to name a few
When you refer to D1 and D2 - what does that mean? I think you are referring to the pipes from the valve but is the "D" for down? Thanks.

There's one other thing - they didnt remove the carpet in the airing cupboard when they changed the cylinder - so now the cylinder sits unevenly - part on the carpet and part off (due to the difference in cylinder sizes). You would have thought they could see that when they put it on!
 
Last edited:
When you refer to D1 and D2 - what does that mean? I think you are referring to the pipes from the valve but is the "D" for down? Thanks.

the pipe from the valve that they changed

1621455135500.gif
 
Hi, In terms of registering the work with building control how does that work? Is the installer meant to notify the council? How quickly will it show up with the council so that I can check they met the G3 requirements? Thanks for your input.
 

Reply to Solar Thermal Cylinder Installation in the Renewables area at PlumbersForums.net

Similar plumbing topics

We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is...
Replies
5
Views
560
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
462
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
285
PSxxxxxx
P
Hello I am looking to install a slimline dishwasher (integrated) into a cupboard in my kitchen. The depth of the dishwasher is 550mm and the...
Replies
22
Views
609
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock