round the exes who complained that her DHW was not working. Greenstar system boiler pressurised system was low pressure so I topped it up. There are 2 dials on the boiler one central heating and one for DHW. Read that the dhw dial only works if there is a diverter valve in the boiler but as there is a three port and two zone valves near the pressurised cylinder I assumed that there wasn't so only the central heating knob would work. The boiler fires fine with this on any setting bar frost stat. there are two danfoss stats and a controller by the boiler but no option for hot water only. I figured if the states were off or less than 10 degrees upstairs and down that the main diverter valve would work however it doesn't. There are TRVs but surely on such an expensive and complicated pressurised system with zone valves there must be a way of having hot water only other than turning off all the TRVs.

Any advice please

Thanks

eddie
 
Hi thanks will try to get some. Out of curiosity (lucky i don't have a cat) why does an unvented cylinder need a two port on the hot water side. And what is meant by seperate controls.

Thanks eddie
Unvented cylinders require a physical restriction on the primary circuit in the event of an overheat, a three port valve can not provide this as they rest open on the hot water port. A motor open, sprung return 2 port valve is required, when the overheat stat triggers, it cuts the power to the valve and it closes itself.

Separate controls means it must have a dedicated time and temperature channel for the hot water. I.e a timer and cylinder stat (with built in manually resettable o/heat cut out).
 
Not necessarily, some may have a three port with a two port fitted after, but to me that says the installer was lazy/not confident at wiring. But they all should have a 2 port, powered via a cylinder stat with a manually resettable overheat cut out.

Yours should have one, checked it hasn't tripped. If it has, you should get it seen to by a plumber qualified to work on Unvented Cylinders.
 
Do it right or just don't bother.

Alright for you perhaps, but what's wrong with 3 port and 2 ports being utilised. Yes it's not ideal but it would work.

Yes it 'appears' as though you know your stuff, but seem to be a little missing on the practical and common sense required in the 'real world'.
 
In the real world I supervise the jobs and replace shoddy work all day long, correct other people shortcuts at customers expense. 22mm 3 port limits the throughput of system and makes difficult to identify problems. All it would take is 3 bits of tube and a tee! Not like that's going to loose you the job is it?
 
Thank you for editing the rude word out Leo.

However, everyone wind their necks in now please before I turn into a Stroppy Croppie!
 
Status
Not open for further replies.

Reply to right here it goes in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock