help needed need wiring diagram 4 pumped zones all on stats and work alone but need boiler pump over run to work on atleast one of the zones thanks
 
Need more info (If you know the exact components, that would be very helpful):

1. Is each zone separately timed?

2. If yes, separate timer or programmable stat?

3. Which boiler (make and exact model)?

If the boiler uses pump overrun, then the pump will be wired directly to the boiler. So you will need an Automatic Bypass Valve fitted after the pump and before the zone valves.
 
Status
Not open for further replies.

Reply to pumped zone wiring in the Plumbing Zone area at PlumbersForums.net

Similar plumbing topics

I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler...
Replies
1
Views
195
Hi all. Hope you have all been keeping well. A while back I decided I only wanted to fit one brand of boiler and decided on Viessmann due to...
Replies
9
Views
329
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
226
Hello all, I'm would like to extend an existing outside tap to another point in the garden. I'm about to pour a concrete patio and was hoping to...
Replies
6
Views
290
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
464
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock