- Messages
- 2,233
http://www.ukplumbersforums.co.uk/g...forum/66714-operating-pressure-appliance.html
I agreed with the point TB made in the above post about not getting an accurate reading due to the gas being fanned in rather than just the gas pressure doing the job, but no one else seemed to agree with him.
So I thought at the first opportunity I would do a test.
- wp at meter with hob on 3 rings - 23 mbar
- wp " " boiler on 60 percent power - 22 mbar
- wp " " " on service max power - 21 mbar
- wp at boiler inlet on 60 percent power - 21 mbar
- wp " " " on service max power - 19 mbar
the pipe was sized and calculated at 0.7 mbar pressure loss.
so I would say the working pressure was 23 mbar as that was the positive pressure of the gas at the meter.
open to opinions, but I agree with the point TB made that a zero governor does create a suction on the pipe/valve and so the pressure taken at the boiler inlet valve, even at the meter is only an approximate figure, that will be lower than the reality.