Hi, thanks in advance for any advice, I've come to change a manifold for the ufh, I have noticed a non return valve on the main dhw outlet on the unvented cylinder
Is this acceptable ?
[automerge]1570704464[/automerge]
Hi, thanks in advance for any advice, I've come to change a manifold for the ufh, I have noticed a non return valve on the main dhw outlet on the unvented cylinder
Is this acceptable ?
My thoughts are no it's not.
 

Attachments

  • 20191010_102755.jpg
    20191010_102755.jpg
    5.4 MB · Views: 28
Last edited:
There's no safety reason why it shouldn't be there and is no different to having non-return valves anywhere else on the hot distribution side of the system. Do you have a secondary return (pumped circuit) on your system?
 
Unless you can find a decent explanation for why it's there I don't think it's necessary but at the same time it's not really doing any harm either.

It would be interesting to know the reasoning behind it being fitted there though.
 
Probably a tmv/ mixing valve causing an issue. Is your cold water alot better than your hot? Pressure wise?

Many tmv's have problems if theres a different between the hot and cold.
 