Just read your thread "water not hot after changing room thermostat" when you had the same DHW problem, you said in one post that when reheating the store without a CH or DHW demand that the boiler was cutting in/out every 3 to 4 minutes, your boiler stat was set to 77C which means the burner was tripping at 82C with the green circ pump continuing to run (correctly). this cycling while the store is heating up doesn't seem quite right IMO, if the store stat is set to say 60C then the boiler should run continuously IMO until this temperature is reached which means that the flowrate should be sufficient to maintain a dT of 17C to allow continuous boiler firing up to the store stat setting of 60C, so a 30kw boiler will require a flowrate of 25.3 LPM to allow the boiler to fire at 100% output, if the flowrate is half this at say 12LPM then the boiler will just modulate to 50% power to maintain 77C flow temperature. I don't know what the rated output & the minimum output of your boiler is but say its 7kw minimum then that can only mean IMO that the flow rate is far too low (theoretically, only ~ 5LPM at 7kw ) to prevent the boiler tripping at 82C and probably well before the cylinder stat is satisfied