I have issue with the Ideal Independent 30 - rated at 33.7kw gross (30.4 nett)

The working pressure at the meter is 21mbar, and at the test point on the isolation valve only 18mbar. Clearly over the 1mbar drop allowed in BS6891. The MI mentions a pressure drop between the external gas cock could further reduce the operating pressure when measured at its test point however as the test point is part of the cock, I cannot see how this can be that restrictive. Has anyone else found the gas test point under the ideals give a restricted reading?

I have gas rated the boiler and obtained a measurement of 2.91m3/hr. The MI show a gas rate of 3.13m3/hr (based on a lower cv of 38.7), so around 7% below MI but within a tolerance -10% / +5%

I have rechecked the pipework sizing, and calculate a 0.74mbar drop from the meter to the end of the 22mm. The final 0.4 metres is reduced to 15mm to supply the boiler with 1 elbow (effective length 0.7m) – This is outside the range of the chart which shows a max of 2.90m3/hr over 3m for 15mm – even at this rate it would cause a drop of 0.23 – total of 0.97 mbar over the system, which is within limits.

Without fitting a test point on the pipework, it not possible to confirm pressure loss over the pipework.

As I am achieving a gas rate within a -10% tolerance, and 18mbar pressure (within the MI specification), is the supply undersized, or are the readings some peculiarity of the ideal isolator test point? Would it be worth fitting a test point on the pipework to confirm? In this event, the final 0.4m of 15mm with elbow might as well be upgraded to 22mm - this will gain approx 0.2mbar.

If undersized, obviously, I want to try to avoid having to upgrade the 22 to 28mm, and I suspect that the final 0.4m of 15mm should be upgraded to 22mm with a 22mm elbow before the reducer. This should gain around 0.2mbar.


 
Last edited by a moderator:
Wow, very thorough. IMHO you are looking too deep into this issue, I would ask;
1. Is the boiler working satifactorily?
2. Are all of the measurements (working pressure/CO/CO2/Ratio) within specified limits?
3. IS IT SAFE?
If the answer is yes, then just make a note on the BENCHMARK paperwork or Gas Safety Cert to show you have noted it and have made a decision based on sound engineering judgement, sorted.
 
I have issue with the Ideal Independent 30 - rated at 33.7kw gross (30.4 nett)








What would others suggest?

I would suggest that you take the extensive advice given to you on the
other forum (diy not) given to you!
 
Status
Not open for further replies.

Reply to Ideal Logic - low inlet working pressure in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, basic question, any insight much appreciated. Looking to have an outdoor tap in my front porch fed from 15mm pex coming up from suspended...
Replies
6
Views
307
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason...
Replies
3
Views
344
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
470
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock