Jock Spanners

Plumbers Arms member
Plumber
Gas Engineer
Messages
208
Evening all,

I've been to service an Ideal Logic Combi 30 today and when I tested the working pressure at the inlet it was only 10mb on maximum rate. The WP was 20mb at the meter. The analytics were spot on and the gas rate 3m/hr. The pipework is correctly sized and there doesn't appear to be any blockage. I had a similar result (15mb) with another Logic. When I ran Ideal technical they said it was okay. So much for a one millibar drop! Has anyone else had a similar experience with a Logic?

Jock
 
4.5mbar on the logics drop due to gas valve resistance

i would say filter blocked or gas pipe too small
 
The test point under the boiler on the valve?
Ideal allow about 1.5mb loss at this point, plus your 1mb on pipework
Sounds like undersized pipe
 
Its in the book
Because its a 15mm tail and 15mm-1/2" valve its slighly restrictive

you cant test at the internal gas valve
 
Sometimes, people solder a 22mm reducer onto 15mm that’s buried in the floor, as close to the floor as possible. It might look like 22mm but if a section of pipe is in the floor or hidden, I’d bet it’s 15mm.
 

Reply to Ideal Logic Combi - Low Working Pressure in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock