Plumbers Arms member
Plumber
Gas Engineer
Messages
5,076
Just back from a 3 week holiday travelling around Europe and went to a Boiler service for my first job, Potterton SE boiler customer been in house 2 years first time they've had it checked, gave them the good news once I checked it out. Boiler looks at least 8 years old.

ratio 0.0125
CO 1098

air intake
o2 17%
ratio 0.006

not enough free flowing clean air and when you went out to flue it completely stunk of gas, customer also reported odd smell of gas when boiler on(tightness test passed) I see no other option but to replace boiler with plume kit to divert to a more open area, that window was into the kitchen and was openable.





image.jpgimage.jpg
 

Attachments

  • image.jpg
    image.jpg
    25.1 KB · Views: 73
  • image.jpg
    image.jpg
    28.7 KB · Views: 69
  • image.jpg
    image.jpg
    24.7 KB · Views: 53
flue looks like its a performa? probably vitiating like mad on that flue location
 
Status
Not open for further replies.

Reply to ID from installation in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is...
Replies
5
Views
538
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
421
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock