Hi all,can any one advise me please?

I have a back boiler with an indirect system.
There is no thermostat on the hot water tank, and the hot water is in my opinion is far to hot. I have small children and this worries me. I have turned down the boiler thermostat to 3 as well.

Is there any way of controlling the water temp better?
can i fit a thermostat to the tank and a 2 way port valve on the pipe from the boiler to the tank to shut off when the thermostat reaches the set temperture? Or will this shut off the radiaters as well.

Thanks Mark
 
i take it its gravity hw and pumped heating.
you can turn it in what is called a c plan.
which is to fit a cylinder stat. and a 2 port zone valve (motorised valve) into the cylinder return pipework.
then you can have control over your hw and temp.
 
i take it its gravity hw and pumped heating.
you can turn it in what is called a c plan.
which is to fit a cylinder stat. and a 2 port zone valve (motorised valve) into the cylinder return pipework.
then you can have control over your hw and temp.

I think so there is a pump next to the back boiler which i presume is for the CH.
the cylinder return would that be the upper of the 2 large bore (28MM?) pipes on the the tank?

When this port valve is closed the heating would be unaffected?

Thanks mark
 
I think so there is a pump next to the back boiler which i presume is for the CH.
the cylinder return would that be the upper of the 2 large bore (28MM?) pipes on the the tank?

When this port valve is closed the heating would be unaffected?

Thanks mark


thanks ajs heating could you confirm these points for me
regards mark
 
Hi all,can any one advise me please?

I have a back boiler with an indirect system.
There is no thermostat on the hot water tank, and the hot water is in my opinion is far to hot. I have small children and this worries me. I have turned down the boiler thermostat to 3 as well.

Is there any way of controlling the water temp better?
can i fit a thermostat to the tank and a 2 way port valve on the pipe from the boiler to the tank to shut off when the thermostat reaches the set temperture? Or will this shut off the radiaters as well.

Thanks Mark

lol. doesthis help ?
 
yes the pump is only for heating.
the 28mm pipes to the cylinder are flow/return. useally the top will be flow bottom return.
but can sometimes be other way round on gravity. you can check when the system is fully cold and then with just hw on see what one gets hot first.

this is how a c plan works/wiring.
and no it won't afect your heating just give you control over the hw temp.

Systems
 
yes the pump is only for heating.
the 28mm pipes to the cylinder are flow/return. useally the top will be flow bottom return.
but can sometimes be other way round on gravity. you can check when the system is fully cold and then with just hw on see what one gets hot first.

this is how a c plan works/wiring.
and no it won't afect your heating just give you control over the hw temp.

[DLMURL="http://www.ukplumbersforums.co.uk/redirector.php?url=http%3A%2F%2Fcontent.honeywell.com%2Fuk%2Fhomes%2Fsystems.htm"]Systems[/DLMURL]

Thanks AJS, I'm not a plumber obviously lol, but can tackle most things myself armed with some helpful info from people such as you cheers.
would you mind if i posed another question to you about my back boiler?
 
Last edited by a moderator:
Status
Not open for further replies.

Reply to Hot water temperture control? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
My disabled daughter’s hot water has stopped working. It’s a relatively modern Potterton boiler with an indirect sealed hot water system and a...
Replies
12
Views
874
Afternoon. I have an issue with no water flow from any of the hot taps in the house, I can't seem to find a solution to the issue. System is a...
Replies
11
Views
345
  • Question
Hello, I am fitting new taps and a shower mixer in my en-suite and was looking to isolate the hot water pipes. I have an unvented indirect...
Replies
2
Views
632
Hi, I have a Vailant EcoTec Boiler with a Megaflo. These are controlled by a Honeywell controller. I have one 3 port diverter, where one of the...
Replies
5
Views
261
First post as I can not figure this one out. I have a hot water boiler heating system, gas fired, with an HTP SuperStor indirect hot water tank...
Replies
2
Views
397
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock