Wonder if I could have some pointers with this boiler.

Flow switch is not being pushed out, with pump running. Pump rotation is strong (checked through the bleed screw), also taken out to check impeller which is securely attached.

When switch manually activated boiler kettles.

When flow and return valves isolated, pump pushes out rod to activate switch. Boiler obviously kettles.

I'm thinking it is a block main hex, any pointers? Thanks in advance. Nuran
 
Could be Blocked primary hex, and or primary flow pipe, check the DHW hex while you've got it drained down.
 
Thanks guys, im back there on Monday so will check dhex and diaghpram.

@jtsplumbing. Yes it's a hard water area.

Now re dhex and split diaghpram. Dhex isn't in play is it if CH is called for. Unless div is stuck and trying to push through dhex.

And the diaghpram, suppose could be a split. Hence only activating when increased pressure when flow return closed.

Still doesn't explain the kettling when with pump running and switch manually activated.
 
Thanks guys, im back there on Monday so will check dhex and diaghpram.

@jtsplumbing. Yes it's a hard water area.

Now re dhex and split diaghpram. Dhex isn't in play is it if CH is called for. Unless div is stuck and trying to push through dhex.

And the diaghpram, suppose could be a split. Hence only activating when increased pressure when flow return closed.

Still doesn't explain the kettling when with pump running and switch manually activated.

either ch diaphragm has split ,the small one at the back,or the hole under its blocked get one of these in advance,you also need a stubby slot driver and a 8mm spanner Baxi Combi 105HE Central Heating Diaphragm Kit 5111138 NEW
 
Thanks Gas Man, as you said. It was the blocked up hole under the diaphragm. The existing one was fine, although changed anyway.
 
Have you checked the filter on the return and the primary thermistor on the flow pipe from heat ex which is a wet pocket some times cap can get caught at this point
 
Have you checked the filter on the return and the primary thermistor on the flow pipe from heat ex which is a wet pocket some times cap can get caught at this point

have a gander at the post above yours, all fixed
 
Status
Not open for further replies.

Reply to Flow switch not activating Baxi Combi 80Eco in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello all, I have a WorcesterBosch Greenstar 42CDi classic combi, which is providing DHW fine, but not heating. Was working fine in spring...
Replies
11
Views
1K
Hi Folks, I have a challenge with a Main Eco Elite 30 Combi which is short cycling on the CH. Water works fine. As soon as you have call for...
Replies
6
Views
434
Hi, As per the thread title, I have an Ideal Logic Combi 30 and I am having a problem with the pump, which keeps activating without any DHW/DCH...
Replies
2
Views
1K
Hi, Just checking I'm not talking rot. Today I visited a house with a Baxi 228 combi boiler. The technical spec for the DHW output is shown in...
Replies
6
Views
1K
R
I just had installed a Navien NPE-2 with built in recirculator pump. I have a dedicated return line. The check valve for the recirc is built into...
Replies
0
Views
344
Rogelio
R
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock