Discuss E133 on Main Combi 25 Eco in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.

nutty_jah

Gas Engineer
Messages
35
So, I'm having an issue with this reoccurring E133 fault on this boiler installed only three months ago.

Initially it was locking out after four attempts of lighting with E133. Sometimes it would light but with explosive ignition.

Looked on previous posts for advice, and have checked the spark electrodes spacing, electrode wire continuity, inlet gas pressure (20mb) and gas valve adj, which were out.

Now the explosive ignition and initial failure to light have been resolved. But apparently now it locks out to E133 after half hour to hour of CH operation.

I have a feeling it's rectification issue, but would it register for a time then suddenly drop to lock out?

I'm back there tomorrow. Any pointers will be well appreciated. Thanks.
 
Check the meter regulater is ok but if it's 3 months old get them out for waranty, also check for loose or damaged cables
 
Last edited:
Test at the meter with the boiler at full rate and make sure you got a stable reading and it doesn't drop like a stone or bounce about
 
Thanks silentmike, lastly the screenshot of the following: is that the new flame sensing probe. Sure when I pulled this one out to set the spark gap, the flame sensing was a stubby steel probe.
 
Are there MI's handy as to the lock-out of E133
Three month old, sound like manufacturer tech issues
Is there a re-set. ??
 
Just a quick update on this. Went again today, pressure from the Meter fine with boiler running at max.

PCB giving our 230v to gas valve, yet valve working intermittently on initial ignition.

Called heat team and suggested change of gas valve, they will out tomorrow. Let's see what they put it down to.

Thanks for all advice offered.
 
Brilliant.
Thanks for returning the news nutty_jah
Wishing you a merry Christmas!
And happy new year...
 
there seems to be an issue with a batch of boilers rolled out recently. i fitted 2 boilers within a week and i had e133 fault codes on both one was the spark ignition fault other electrodes heateam sorted it out
 
Status
Not open for further replies.

Reply to E133 on Main Combi 25 Eco in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi Folks, I have a challenge with a Main Eco Elite 30 Combi which is short cycling on the CH. Water works fine. As soon as you have call for...
Replies
6
Views
435
A
We have a vaillant combi boiler that over ~ 2yrs loses a bit of pressure, and recently after 2 weeks away and no use the system would not fire and...
Replies
2
Views
513
Good afternoon Guy's & Girl's, So I have a Baxi 630i that is showing a e133 fault. Upon hours of extensive research it is an ignition fault that...
Replies
21
Views
3K
  • Locked
I have a strange fault with a Vaillant EcoTec combi-boiler. It's 100% reliable whenever the heating is called for, ie. by the room-stats. It's...
Replies
7
Views
915
In our Village Hall we have a Ideal Concord CXS/SD40/H central heating boiler. This was installed new when we had an extension built and the...
Replies
10
Views
1K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock